In an LT pole, the line voltage is 415V. How is it
converted to 230V into the house via the service cable?
Answers were Sorted based on User's Feedback
Answer / chandrashekar g
Actually there will be 4 wires ie 3ph 4wire system
for 230v supply can be achieved by taking one phase and one
neutral from it.
Is This Answer Correct ? | 31 Yes | 0 No |
Answer / p.s,suresh
ph-ph voltage 415V.(3 Ph)
ph-Ne voltage 230V (1 Ph)
Is This Answer Correct ? | 28 Yes | 0 No |
Answer / jitender kotwal
From distrubation transformer we get three phases and one
netural (due to Star connection) these four wire(three
phases and one netural)are layed over head on LT poles and
for houseonly one phase along with netural is used and no
convertor is used as phase to netural voltage is 220volt
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / anand mishra
We can use 1ph-1neu for Covertion of 415v to 230v
Is This Answer Correct ? | 8 Yes | 1 No |
From distrubation transformer we get three phases and one
netural (due to Star connection) these four wire(three
phases and one netural)are layed over head on LT poles and
for house only one phase along with netural is used and no
convertor is used as phase to netural voltage is 230volt
between R -y- b phase voltages are 415 - 415-415 called
as line value where as between phase and neutral it will
be 415/1.732 = 239 approximately 230v called as phase value
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / a.y.naidu
actually transformer has two windings i.e primary and
secondary.primary is delta connected.secondary is star
connected.in delta 3 wires(3 ph) in star 4 wires(3 ph and
neutral).out come is
phase -phase--- 415V
phase -neutral--230V
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shahzad
line voltage=the voltage between two phases=415v
phase to neutral voltage=line voltage/1.732=415/1.732=239.6v
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / soutrick chakraborty
Actually there will be 4 wires, 3ph 4wire system
for 230v supply can be achieved by taking one phase and one
neutral from it by lt pole but the four wire is come from lt
side, and the distribution transformer is delta star connection.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kranthi kumar k
ph-ph voltage 415v and ph-neutral voltage is 230v.only phase
wires runs in HT side.The nuetral wire is taken from the
step down transformer secondary side.So we can supply 230v
to houses by means of phase and neutral wire
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / a.bala
u can take a 230 v supply by using one Phase Segregation
Distribution board
Is This Answer Correct ? | 4 Yes | 9 No |
Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?
why exciter frequency 150 Hz ?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
what is the difference between the following 2 situations ? 1)Line & Neutral=240V Line & Earth=230V Neutral & Earth=10V 2)Line & Neutral=230V Line & Earth=240V Neutral & Earth=10V
Give two basic sprrd control scheme of DC shunt motor.
what is slip resistance? how much its value in 110 kw motor? why voltage is varied in vvvf drive ?
How do u term the word 'OF' in Megger Testing???
what is saturation? what role it plays in operation of ct's,motors etc and how its affects the behaviour of the same.
How can I calculate the trnaformer effciency at different loading condition?
What are the two types of transistor and how they are made?
Is there any difference between load based power plant and coal based power plant?
Why the colour of insulator is always is chocolate in colour?