In an LT pole, the line voltage is 415V. How is it
converted to 230V into the house via the service cable?
Answers were Sorted based on User's Feedback
Answer / chandrashekar g
Actually there will be 4 wires ie 3ph 4wire system
for 230v supply can be achieved by taking one phase and one
neutral from it.
| Is This Answer Correct ? | 31 Yes | 0 No |
Answer / p.s,suresh
ph-ph voltage 415V.(3 Ph)
ph-Ne voltage 230V (1 Ph)
| Is This Answer Correct ? | 28 Yes | 0 No |
Answer / jitender kotwal
From distrubation transformer we get three phases and one
netural (due to Star connection) these four wire(three
phases and one netural)are layed over head on LT poles and
for houseonly one phase along with netural is used and no
convertor is used as phase to netural voltage is 220volt
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / anand mishra
We can use 1ph-1neu for Covertion of 415v to 230v
| Is This Answer Correct ? | 8 Yes | 1 No |
From distrubation transformer we get three phases and one
netural (due to Star connection) these four wire(three
phases and one netural)are layed over head on LT poles and
for house only one phase along with netural is used and no
convertor is used as phase to netural voltage is 230volt
between R -y- b phase voltages are 415 - 415-415 called
as line value where as between phase and neutral it will
be 415/1.732 = 239 approximately 230v called as phase value
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / a.y.naidu
actually transformer has two windings i.e primary and
secondary.primary is delta connected.secondary is star
connected.in delta 3 wires(3 ph) in star 4 wires(3 ph and
neutral).out come is
phase -phase--- 415V
phase -neutral--230V
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shahzad
line voltage=the voltage between two phases=415v
phase to neutral voltage=line voltage/1.732=415/1.732=239.6v
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / soutrick chakraborty
Actually there will be 4 wires, 3ph 4wire system
for 230v supply can be achieved by taking one phase and one
neutral from it by lt pole but the four wire is come from lt
side, and the distribution transformer is delta star connection.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kranthi kumar k
ph-ph voltage 415v and ph-neutral voltage is 230v.only phase
wires runs in HT side.The nuetral wire is taken from the
step down transformer secondary side.So we can supply 230v
to houses by means of phase and neutral wire
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / a.bala
u can take a 230 v supply by using one Phase Segregation
Distribution board
| Is This Answer Correct ? | 4 Yes | 9 No |
What is Tan Delta Test
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
How to use earthing on shipments.
What are the voltage values for LT,HT,EHT and other voltages??
why the earth terminal of the three pin plug we are using bigger than the others?
If you touch at the end welding machine, will you have shock ?
Give details of your interested designation, the post you are interested to serve the company better and explain why you think you can serve the company better in such position if employed?
why do we require two lines one phase and a neutral for an ac transmission..is neutral potential zero..?if yes y carry a neutral line from generating station itself...why dont we take it from ground
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
figure of phasor diagram of transformer when full load or no load ?
what is differance between dirty earthing and clean earthing and their applications
How to take vector group test for Ynd11 transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)