Answer / jince

Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same

2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER

In order to share the load evenly we must control the voltage and frequency of individual DG's constantly

And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs

For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required


For clarification please reply

Is This Answer Correct ?    3 Yes 0 No

725KW Three DG set Synchronised but DG no-1 power showing 750KW DG n0-2 power showing 500KW DG no-..

Answer / tango

synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity

Is This Answer Correct ?    2 Yes 2 No

725KW Three DG set Synchronised but DG no-1 power showing 750KW DG n0-2 power showing 500KW DG no-..

Answer / kj

If the DG's are the same rating then the load sharing is
out of adjustment.

Load sharing can be by speed droop (see answer above) or by
load sharing controller.

Adjustment of either of these can rectify problem.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

in railways why we use the power in 10,20 30kv,why not in the multiple of 11kv

2 Answers  


if we convert kva into Ampers,which one formula use by us,pls tell me?

7 Answers   ABB,


What is Earth Fault and Over current Fault.

1 Answers  


What is working principle of ACB and VCB?

9 Answers   Greenko, HCC,


relation between power station capacity and voltage level?

0 Answers  






Current Transformer's star point must face the protected object for the relay operation?

2 Answers   Siemens,


when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil

0 Answers  


When Neutral exceeds or equals the phase current in both single phase * three phase system?

1 Answers  


for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?

0 Answers  


Dry type transformers

0 Answers  


my question is Megger of cable insulation or swgr board meggerring some values in one day 50mohms,some other day checking different values(20Mohms). this tell that some person tell that that values ok. how to identify the megger value is correct. pls tell me the answer.

2 Answers  


Dear All please ive me ur ideas... What is the major diff between cu conductors and Al conductors ?

3 Answers   MX Technology,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)