725KW Three DG set Synchronised but DG no-1 power showing
750KW DG n0-2 power showing 500KW DG no-03 showing 500KW.
DG is Shynchronised but why this different power showing?
Answers were Sorted based on User's Feedback
Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
| Is This Answer Correct ? | 2 Yes | 2 No |
If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?
What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor
why the genearation of electricity always in form of sine wave only ??? why not cosine wave ???
How to calculate the cable size (XLPE)for suitable to 120KW load (if Motor or heaters etc)
Negative feedback circuit is an implication of ? -Shunt shunt -Shunt series -series series
Without seeing the nameplate descriptions of a rotating machine,Is it possible to say which one is a motor and which one is a generator? How would you certain this?
* Signal transmission in sky wave propagation is due to ? a) Reforction of wave b) Reflection of wave c) Pierus through Inosphere d) None and Reason for this is????
How i can decide that HVDC line is best for transmission.
How to calculate the phase to phase clearness of HT /// LT bus bar?????
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
what will be the difference on output when 3phase I.M. is given a delta or star supply?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)