Answer / prakash suhane
Rating of cable depend on various factors like
1) Size of cable
2) No.of cores
3) Type of Insulation
4) Laying in air/ underground
5) Multi strand or single strand
Is This Answer Correct ? | 144 Yes | 7 No |
Answer / vignesh
Current rating shall be decided by
* load requirement
* Power factor
* Voltage rating
Is This Answer Correct ? | 71 Yes | 7 No |
There is no any thumb rule, therer is a standard table from
which we can know the capacity of the cable.
The current carrying capacity is depend upon the size of
conductor(Cross sectional area)
Is This Answer Correct ? | 71 Yes | 13 No |
Answer / hdn electrical
There is no 'rule of thumb'. The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.
The tables in BS 7671 will show optimum carrying capacities,
but will then be subject to de-rating factors such as
ambient temperature, grouping, how it's fixed in/on a wall
or if it will be covered by insulation.
If you are unsure you should contact a qualified electrician.
Is This Answer Correct ? | 22 Yes | 4 No |
Answer / gurupirit singh
The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.And also depend on
insulstaion & cooper of wire.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hariom
There is no 'rule of thumb'. Every manufacture provide their cables current carrying Data.It is almostly Same as per ISI.The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / simon
The rule of thumb for current carrying capacity of copper
wire is 6 amperes per square millimeter of cross-sectional
area for an insulated, uncooled conductor.
Therefore the following applies:
1.0mm 6A
1.5mm 9A
2.5mm 15A
6.0mm 36A
Note that with air cooling, such as within an electric motor
or generator, the current carry capacity of the conductor
may be as high as five times the figures above (up to
30A/mm2) but is dependent on the efficiency of the cooling.
Is This Answer Correct ? | 26 Yes | 31 No |
Answer / sonu
current carrying capacity of wire's of
2.5 sq.mm=29amp
4.0 sq.mm=37amp
6.0 sq.mm=48amp
10.0 sq.mm=66amp
Is This Answer Correct ? | 28 Yes | 38 No |
Answer / arun kr. singh
The Thumb rule is:
Size of cable x 4 = Current rating of cable.
e.g rating of 2.5mmsq cable is: 2.5x4=10A
for 4mmsq cable is: 4x4=16A
6mmsq cable is: 6x4=24A
10mmsq cable is:10x4=40A
Is This Answer Correct ? | 7 Yes | 23 No |
What is difference between PLC and SCADA
13 Answers Uflex, Vimal Fire Controls,
On which side, taps are provided in tap changing transformers and why?
Why do we require transformer with less specific weight if supply frequency is increased?
why power of fm is weaker than am?
when we increase load , current drawn from source also increases why ?
why are transformer rating in MVA
What will happen if we parallel two transformer with different %impedace?
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
what is form factor.and rms value..
Explain advantages of storage batteries
How do i calculate sizing of transformer on didstrubution load for high rise building.What should be MVA Rating of MV Panel feding by 122 kv.
How to synchronization will be done between two DGs ?