Answer / srij21
Link is provided at a Neutral common point in the circuit
from which various connection are taken for the individual
control circuit and so it is given in a link form to
withstand high Amps
But in the case of Fuse in the Phase of AC circuit it is
designed such that the fuse rating is calculated for the
particular circuit (i.e load) only.So if any malfunction
happen the fuse connected in the particular control circuit
alone will blow off.
| Is This Answer Correct ? | 63 Yes | 8 No |
Answer / jamshid al rahman
This can be explained easily by a small example.Assume u are going to use an iron box with fuse on both neutral and phase,Due to some internal problem the fuse blows first which is connected in neutral which prevents the equipment and source supply from more danger now if you are touching the body of iron box having leakage fault,your body acts as a path to flow current from phase to iron box and from there through your body to the ground here the circuit get closed,you will be in hazard.So keep fuse only in phase (This is only for AC supply)
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / k.prakashchandra
And also, if neutral fuse blows off all the single phase
appliances will be deprived of supply.
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / cyber4india
The neutral should be solid and only Link should be provided
in neutral as if fuse is provided, in case of shock, it will
blow due to overload, but the supply will be available
through phase and the purpose of fuse is defeated.Fuse is
provided in the phase supply to protect the overload
conditions arising due to short ckt, shock, etc
In some case(domestic wiring) the neutral also contains
some potential due to unbalance of load in the supply (3
Phase). This holds true even if you are using the one out of
three phase . The neutral is displaced due to uneven
loading. Hence for any purpose of working, neutral Links
should also be disconnected along with the fuse in phase supply.
| Is This Answer Correct ? | 11 Yes | 13 No |
whats was the problem if neutral and earth got 2volt from the ups output
difference between moore and mealy model
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
What is the deference between earth fault & earth leakage
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
a simple c++ program to calculate simple interst with its data members as private
the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????
why we are using Load factor?
what is the electrical?
Can a generator runs after getting 1st stator earth fault.
How To Convert Apparent Into Real Power Without Knowing Reactive Power?
last week we did the REF relay test by closing single pole (R phase) of CB and apply 380V at the primary of delta transformer. we get 33A at the primary of the R phase star end. but we get 380A at both R an B in delta side. how and why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)