Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why link is provided in neutral of an ac circuit and fuse
in phase of ac circuit?

Answers were Sorted based on User's Feedback



why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?..

Answer / srij21

Link is provided at a Neutral common point in the circuit
from which various connection are taken for the individual
control circuit and so it is given in a link form to
withstand high Amps

But in the case of Fuse in the Phase of AC circuit it is
designed such that the fuse rating is calculated for the
particular circuit (i.e load) only.So if any malfunction
happen the fuse connected in the particular control circuit
alone will blow off.

Is This Answer Correct ?    63 Yes 8 No

why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?..

Answer / jamshid al rahman

This can be explained easily by a small example.Assume u are going to use an iron box with fuse on both neutral and phase,Due to some internal problem the fuse blows first which is connected in neutral which prevents the equipment and source supply from more danger now if you are touching the body of iron box having leakage fault,your body acts as a path to flow current from phase to iron box and from there through your body to the ground here the circuit get closed,you will be in hazard.So keep fuse only in phase (This is only for AC supply)

Is This Answer Correct ?    15 Yes 9 No

why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?..

Answer / k.prakashchandra

And also, if neutral fuse blows off all the single phase
appliances will be deprived of supply.

Is This Answer Correct ?    8 Yes 6 No

why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?..

Answer / cyber4india

The neutral should be solid and only Link should be provided
in neutral as if fuse is provided, in case of shock, it will
blow due to overload, but the supply will be available
through phase and the purpose of fuse is defeated.Fuse is
provided in the phase supply to protect the overload
conditions arising due to short ckt, shock, etc
In some case(domestic wiring) the neutral also contains
some potential due to unbalance of load in the supply (3
Phase). This holds true even if you are using the one out of
three phase . The neutral is displaced due to uneven
loading. Hence for any purpose of working, neutral Links
should also be disconnected along with the fuse in phase supply.

Is This Answer Correct ?    11 Yes 13 No

Post New Answer

More Electrical Engineering Interview Questions

whats was the problem if neutral and earth got 2volt from the ups output

1 Answers  


difference between moore and mealy model

2 Answers   Google, IBM, TCS,


During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?

4 Answers  


What is the deference between earth fault & earth leakage

1 Answers  


How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer

2 Answers   ABB,


a simple c++ program to calculate simple interst with its data members as private

0 Answers   L&T,


the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????

1 Answers   ABB,


why we are using Load factor?

0 Answers  


what is the electrical?

0 Answers  


Can a generator runs after getting 1st stator earth fault.

0 Answers  


How To Convert Apparent Into Real Power Without Knowing Reactive Power?

0 Answers  


last week we did the REF relay test by closing single pole (R phase) of CB and apply 380V at the primary of delta transformer. we get 33A at the primary of the R phase star end. but we get 380A at both R an B in delta side. how and why?

1 Answers   Siemens,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)