What is the use of doing meggering for a cable
Answers were Sorted based on User's Feedback
Applying" a voltage, With two conductors that are supposed
to be insulated, the amount of insulation can vary
depending on the thickness of the insulating material, the
amount of moisture, or from being contaminated with an
electrically conductive substance. The insulation could be
thin in one or more spots due to improper manufacture, or
due to overheating, or due to applying excessive mechanical
force, etc. So,
Megging the insulation is intended to
check for any of these imperfections.
When the voltage is applied across two conductors that are
supposed to be insulated, the megohmmeter measures the
current that flows. If the current is lesss than the
specified amount, then the insulation is meeting the
specified minimum. If it fails the test, then there is a
problem such as I mentioned above.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / er.s.ramkumar
Ensure the insulation throughout the cable is good or
not.during the hv test measured leakage current in the
cable is allowable means insulation also good.
| Is This Answer Correct ? | 4 Yes | 1 No |
WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,
what power factor should we maintain to get maximum benefits our organisation load is 10 MW? is it best to maintain the PF at .96 rather than Unity to save electricity bill?
how the vaccum ckt breaker workes..? how the arc is quenching in it?
What is the difference between voltage transformer and potential transformer?
38 Answers ABB, ETA, Maritime Academy, MSEB, Reliance Jio, Voltas, Wipro,
What is the function of lead sheath?
Can we use HRC Fuse inplace of Semiconductor fuse?
why substation ratings are multiple of 11 means 11\33 kv substation
what is the difference between the 94 lockout relay and 86 lock out relay. I have noticed that the 94 lockout relay is activated when the distance realy is activated and 86 is activated when the 87T differential is activated. but why can't the same lockouts be used for both the protection schemes
What is the rating of your substation and what are the different types of substations?
how we can check the CT & VT?
what is isochronous mod? what is voltage drop mode and p.f mode?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)