why ct mensioned 0.5/5p20 plese any reply to me
Answers were Sorted based on User's Feedback
Answer / aju m paulose
0.1, 0.2, 0.5, 1, 3 are Accuracy class
They are used for metering purposes
5P10, 5P15, 5P20 are used for metering and protection purposes
5 indicates Composite error in % and 'P' for protection and 10 means accuracy limit factor...
i.e the CT will have 5% error if the current under measurement is 10 times the normal value
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / balakrishna
ct has 3 classes.ie.
0.2,0.5,1
5p10,5p20
ps
here 0.2, 0.5,1 used for metering classes
5p10,5p20 used for protection like overcurrent & earth
fault purpose
ps class used for the differential/distance protection
Is This Answer Correct ? | 6 Yes | 2 No |
Befor synchronissation of Generator what test to be carried out.pl.specify with reason.
Why mostly GT(Generating Transformer)has only Ynd1 Vector Group?
what are upstream faults and downstream faults in power system
what is phase to phase fault? what is line to line fault?
We have a 33/11kv switchyard having 12.5 MVA power transformer. We export & import power through this transformer. When we export power, the PF will be depend on GRID PF & when we import power the PF will be depend on our load PF. but the problem is that,when neither we export nor import but our 33KV vCB is in close position,our meter read the power factor 0.14 to 0.25 at that moment. So how can be we improve the power factor at that moment.
Hi, I've just got into my electrical engineering course and I need some help with a question of mine here. During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz. From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
I am doing apprenticeship training at HT switch yard in NLC. How can i get electrical c license. ??? What r the rules for getting it as an apprentice? ??
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
What is gross error?
What does bode plots shows?
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
What is plc.