If load is 240 kw & pf is 0.8 lagging, than how to increase
it from0.8 to 1.0(unit),which rating capacitor used, please
give me Calculation. What is effact of consumer & suplier
if pf is lagging or leading with on effect machines/ TF/GE
etc.
Answers were Sorted based on User's Feedback
Answer / ashish kumar rai
We can improve power factor by:-
1) Capacitor
2) Synchronous motor
3) Synchronous Generator
When Power facto Cos(pi)= .8
KW = KW*Cos(PI) = 240
KVA = KW/ Cos (pi)= 300
KVAR = KW*Sin(pi) = 180
When Power factor Cos(pi)= 1
KW= 300
kVA = 300
KVAR= 0
So we use the capacitor of rating of 180 kvar to neutralise
the inductive 180 kvar.
Effect on consumer:-
1) Lower utility fees by:
a. Reducing peak KW billing demand
b. Eliminating the power factor penalty
2) Increased system capacity and reduced system losses in
your electrical system
3) Increased voltage level in your electrical system and
cooler, more efficient motors
Effect on Utility:-
1) It has to generate less poaer
2) Reduced Current Hance Reduced losses
3) Less condutor for transmisssion
4) Less current hence insulating cost
4) Less conductor and insulation decrease cost of
supporting structure
5) High Efficiency
6) More stable system
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / michael
using the formula for cmputing KVAR
KVARcap = KWrating(tan(theta1) - tan(theta2))
where theta 1 is the angel of .8pf and theta 2 is angel of 1.0pf
KVARcap = 240k (tan36.87 + tan 0)
KVARcapacitor = 180KVAR..
that will be the answer.. or using vector solution
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abduljameel
Normally required capacitors will be in KVAR.
Required KVAR = KW (tan pi1 - tan pi2 )
cos pi1= .8
cos pi2 =1
then calculate accordingly
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mohit parmar
first of all u are not supposed to improvethe power factor
to 1.....since, u have to take clearance for sudden
disconnection of loads.any ways if u want to calculate
capaciitance value refer to any hand book of electrical
engineering,,they have the charts telling u the value of
capacitance if u know the present and ur required
value.regarding power factor...it is one of the main
criteria for efficient elctrical system...since it directly
effects the current carried by the system or cables or
equipment at load side.let us suppose there is a motor of
say...15 kw and pf is( case 1:.85and case2:.95)keeping
voltage constant we can see that current drawn in case1 is
1.2 times that of in case 2 so,this extra current for same
wattage generates more heat and hence losses.
| Is This Answer Correct ? | 3 Yes | 2 No |
required kvar= 240 kw x 0.750= 180 kvar
0.750 is the multipling factor.
you have to use 180 kvar capacitor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / furat
A 500KVA 6600/440 transformer has primary and secondary winding resistance of 0,45 ohms and 0,0015 respectively .The iron loss is 2.9KW. Calculate the efficiency of the transformer on a full load and again in half load if the power factor of the load is 0,8 lagging.
| Is This Answer Correct ? | 2 Yes | 1 No |
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
why not feeling shock while touching rotor shaft of induction motor during running condition? during running condition emf induced in rotor.
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
what is a starter ??
what are the protections in 132 kv class electrical systems.....? hw u define that in elctrical terms..? . . .pls answr
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?
1.What is wind span ,wight span and normal span, and what is the difference for 132kv transmission .
Why we use ups battery and dsdb battery in thermal power plant
Why armature rheostat is kept in maximum position?
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
can three phase induction motor rotate with only 2 phases connected
22 Answers Delta, Mannar Company, Suntron,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)