Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If load is 240 kw & pf is 0.8 lagging, than how to increase
it from0.8 to 1.0(unit),which rating capacitor used, please
give me Calculation. What is effact of consumer & suplier
if pf is lagging or leading with on effect machines/ TF/GE
etc.

Answers were Sorted based on User's Feedback



If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / ashish kumar rai

We can improve power factor by:-
1) Capacitor
2) Synchronous motor
3) Synchronous Generator

When Power facto Cos(pi)= .8
KW = KW*Cos(PI) = 240
KVA = KW/ Cos (pi)= 300
KVAR = KW*Sin(pi) = 180

When Power factor Cos(pi)= 1
KW= 300
kVA = 300
KVAR= 0

So we use the capacitor of rating of 180 kvar to neutralise
the inductive 180 kvar.

Effect on consumer:-
1) Lower utility fees by:
a. Reducing peak KW billing demand
b. Eliminating the power factor penalty
2) Increased system capacity and reduced system losses in
your electrical system
3) Increased voltage level in your electrical system and
cooler, more efficient motors
Effect on Utility:-
1) It has to generate less poaer
2) Reduced Current Hance Reduced losses
3) Less condutor for transmisssion
4) Less current hence insulating cost
4) Less conductor and insulation decrease cost of
supporting structure
5) High Efficiency
6) More stable system

Is This Answer Correct ?    6 Yes 0 No

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / michael

using the formula for cmputing KVAR

KVARcap = KWrating(tan(theta1) - tan(theta2))

where theta 1 is the angel of .8pf and theta 2 is angel of 1.0pf

KVARcap = 240k (tan36.87 + tan 0)
KVARcapacitor = 180KVAR..
that will be the answer.. or using vector solution

Is This Answer Correct ?    3 Yes 0 No

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / abduljameel

Normally required capacitors will be in KVAR.
Required KVAR = KW (tan pi1 - tan pi2 )
cos pi1= .8
cos pi2 =1

then calculate accordingly

Is This Answer Correct ?    4 Yes 2 No

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / mohit parmar

first of all u are not supposed to improvethe power factor
to 1.....since, u have to take clearance for sudden
disconnection of loads.any ways if u want to calculate
capaciitance value refer to any hand book of electrical
engineering,,they have the charts telling u the value of
capacitance if u know the present and ur required
value.regarding power factor...it is one of the main
criteria for efficient elctrical system...since it directly
effects the current carried by the system or cables or
equipment at load side.let us suppose there is a motor of
say...15 kw and pf is( case 1:.85and case2:.95)keeping
voltage constant we can see that current drawn in case1 is
1.2 times that of in case 2 so,this extra current for same
wattage generates more heat and hence losses.

Is This Answer Correct ?    3 Yes 2 No

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / sudheer(denso)

required kvar= 240 kw x 0.750= 180 kvar
0.750 is the multipling factor.
you have to use 180 kvar capacitor.

Is This Answer Correct ?    1 Yes 0 No

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rati..

Answer / furat

A 500KVA 6600/440 transformer has primary and secondary winding resistance of 0,45 ohms and 0,0015 respectively .The iron loss is 2.9KW. Calculate the efficiency of the transformer on a full load and again in half load if the power factor of the load is 0,8 lagging.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

how to calculate vfd o/p voltage by frequency

0 Answers   HCL, Orchid,


WHICH TYPE OF TRANSFORMER USED IN SWITCHYARD IN POWER PLANT?

15 Answers   GE, Lanco, NTPC,


in alternator how we can give power to rotor ? its power is AC or DC ?

5 Answers  


What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers

3 Answers  


what are smoke detectors ?

4 Answers   Indian Military Services,


plz send me HPCL apptitude paper.. maulik_elect@yahoo.co.in

0 Answers   HPCL,


What is the material used for the core of a high freiquency transformer?

3 Answers   Videocon,


If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link

0 Answers   Marafiq,


1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.

0 Answers  


Transformer/insulating oil tester(BDV tester)

1 Answers  


In power transmission using open belts or horizontal shafts it is preferable to have the slack side of the belt on the top because

0 Answers   Caterpillar,


How to calculate voltage drop in copper and aluminium cable? I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground. Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)