If load is 240 kw & pf is 0.8 lagging, than how to increase
it from0.8 to 1.0(unit),which rating capacitor used, please
give me Calculation. What is effact of consumer & suplier
if pf is lagging or leading with on effect machines/ TF/GE
etc.
Answers were Sorted based on User's Feedback
Answer / ashish kumar rai
We can improve power factor by:-
1) Capacitor
2) Synchronous motor
3) Synchronous Generator
When Power facto Cos(pi)= .8
KW = KW*Cos(PI) = 240
KVA = KW/ Cos (pi)= 300
KVAR = KW*Sin(pi) = 180
When Power factor Cos(pi)= 1
KW= 300
kVA = 300
KVAR= 0
So we use the capacitor of rating of 180 kvar to neutralise
the inductive 180 kvar.
Effect on consumer:-
1) Lower utility fees by:
a. Reducing peak KW billing demand
b. Eliminating the power factor penalty
2) Increased system capacity and reduced system losses in
your electrical system
3) Increased voltage level in your electrical system and
cooler, more efficient motors
Effect on Utility:-
1) It has to generate less poaer
2) Reduced Current Hance Reduced losses
3) Less condutor for transmisssion
4) Less current hence insulating cost
4) Less conductor and insulation decrease cost of
supporting structure
5) High Efficiency
6) More stable system
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / michael
using the formula for cmputing KVAR
KVARcap = KWrating(tan(theta1) - tan(theta2))
where theta 1 is the angel of .8pf and theta 2 is angel of 1.0pf
KVARcap = 240k (tan36.87 + tan 0)
KVARcapacitor = 180KVAR..
that will be the answer.. or using vector solution
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abduljameel
Normally required capacitors will be in KVAR.
Required KVAR = KW (tan pi1 - tan pi2 )
cos pi1= .8
cos pi2 =1
then calculate accordingly
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mohit parmar
first of all u are not supposed to improvethe power factor
to 1.....since, u have to take clearance for sudden
disconnection of loads.any ways if u want to calculate
capaciitance value refer to any hand book of electrical
engineering,,they have the charts telling u the value of
capacitance if u know the present and ur required
value.regarding power factor...it is one of the main
criteria for efficient elctrical system...since it directly
effects the current carried by the system or cables or
equipment at load side.let us suppose there is a motor of
say...15 kw and pf is( case 1:.85and case2:.95)keeping
voltage constant we can see that current drawn in case1 is
1.2 times that of in case 2 so,this extra current for same
wattage generates more heat and hence losses.
| Is This Answer Correct ? | 3 Yes | 2 No |
required kvar= 240 kw x 0.750= 180 kvar
0.750 is the multipling factor.
you have to use 180 kvar capacitor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / furat
A 500KVA 6600/440 transformer has primary and secondary winding resistance of 0,45 ohms and 0,0015 respectively .The iron loss is 2.9KW. Calculate the efficiency of the transformer on a full load and again in half load if the power factor of the load is 0,8 lagging.
| Is This Answer Correct ? | 2 Yes | 1 No |
how to calculate vfd o/p voltage by frequency
WHICH TYPE OF TRANSFORMER USED IN SWITCHYARD IN POWER PLANT?
15 Answers GE, Lanco, NTPC,
in alternator how we can give power to rotor ? its power is AC or DC ?
What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers
what are smoke detectors ?
4 Answers Indian Military Services,
plz send me HPCL apptitude paper.. maulik_elect@yahoo.co.in
What is the material used for the core of a high freiquency transformer?
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.
Transformer/insulating oil tester(BDV tester)
In power transmission using open belts or horizontal shafts it is preferable to have the slack side of the belt on the top because
How to calculate voltage drop in copper and aluminium cable? I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground. Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)