Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why is shaft current insulation required on large motors &
when should it be checked i.e. before or after assembly?

Answers were Sorted based on User's Feedback



Why is shaft current insulation required on large motors & when should it be checked i.e. befo..

Answer / sunil kumar sinha

Shaft of large motors need to be insulated at one end and
earthed at other end.Due to some unbalance in electrical
system (Which can not be avoided)very small amount of
voltage induces along the rotor shaft. One end of shaft is
normally earthed through carbon brush or through earthed
bearing, hence one end of rotor shaft is anchored at earth
potential and other end will float and experience small
voltage w.r.t earth as voltage is induced along the shaft.
Now the shaft is supported on bearings. One
end of bearing is either earthed if no earthing brush is
provided and the other end support bearing is insulated.The
insulation resistance of shaft, by lifting earthed beating
end of the shaft is to be measured to ensure that the
insulated bearing is healthy. This is to be measured during
assembly of motor because the healthy mess of insulated
bearing can be checked at this stage only.
Further when motor is in operation shaft voltage is to be
measured. Some voltage must appear. If there is no voltage
it indicates that the insulated bearing has also earthed.
this will make path for shaft current to flow through the
bearings. this will result in pitting of babit of bearings
and finally its failure, increase in shaft vibration.
Hence for healthiness of support bearings of motor current
insulation is must and need to be checked periodically for
healthyness of motor rotor bearings.

Is This Answer Correct ?    0 Yes 0 No

Why is shaft current insulation required on large motors & when should it be checked i.e. befo..

Answer / avd

In large motors both bearings needs to be insulated to
avoid flow of current through bearings.This flow of current
is caused in rotor due to high flux in the large motors. If
current flows through bearings there will be pitting in the
bearings and will cause premature bearing failure. To give
path to current, genaraly carbon brushes are used at motor
shaft which are grounded at other end.Hence flow of current
through bearings avoided.
After assembling of motor on bearing padastal both
bearings insulation resistance shall be checked by megger.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

i heard that power factor(PF) is the main concern for industries, if they are maintaining PF around 0.6 they will be fined for that. now the question is, how can they improve the PF ranging between 0.9 to 0.95 which is safe for them i,e escaping from the fine?

5 Answers  


What happen when switch yard one pole not tripe when you tripping the breaker

3 Answers   Adani,


What are thermo couple cables and where they are used.

2 Answers  


Why CTs are connected in star on T/F delta connected winding side & in delta on T/F star connected winding side for T/F differential protection?

2 Answers  


12.5 tons a/c is their how much kva generator can recommend to the customer.

0 Answers  


Why the substation measure in KV but not in the power ratings of transformer.

4 Answers  


what is ALF and ISF in current transformer?

1 Answers  


why v/f ratio to maintain constant in speed control of induction motor?

3 Answers  


What quedtion to ask a electrical maintenance technician?

5 Answers   Bhel, Royal Furnishers,


What do you mean by a phase angel of instrument transformer?

0 Answers  


Can we use 1.1x 2 split air-conditioning at a same time in 2kw power loadar

1 Answers  


what ll happen if neutral is not shorted with phases while doing transformer short circuit test & what ll happen if neutral is connected to ground?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)