Answer / sunil kumar sinha
Shaft of large motors need to be insulated at one end and
earthed at other end.Due to some unbalance in electrical
system (Which can not be avoided)very small amount of
voltage induces along the rotor shaft. One end of shaft is
normally earthed through carbon brush or through earthed
bearing, hence one end of rotor shaft is anchored at earth
potential and other end will float and experience small
voltage w.r.t earth as voltage is induced along the shaft.
Now the shaft is supported on bearings. One
end of bearing is either earthed if no earthing brush is
provided and the other end support bearing is insulated.The
insulation resistance of shaft, by lifting earthed beating
end of the shaft is to be measured to ensure that the
insulated bearing is healthy. This is to be measured during
assembly of motor because the healthy mess of insulated
bearing can be checked at this stage only.
Further when motor is in operation shaft voltage is to be
measured. Some voltage must appear. If there is no voltage
it indicates that the insulated bearing has also earthed.
this will make path for shaft current to flow through the
bearings. this will result in pitting of babit of bearings
and finally its failure, increase in shaft vibration.
Hence for healthiness of support bearings of motor current
insulation is must and need to be checked periodically for
healthyness of motor rotor bearings.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avd
In large motors both bearings needs to be insulated to
avoid flow of current through bearings.This flow of current
is caused in rotor due to high flux in the large motors. If
current flows through bearings there will be pitting in the
bearings and will cause premature bearing failure. To give
path to current, genaraly carbon brushes are used at motor
shaft which are grounded at other end.Hence flow of current
through bearings avoided.
After assembling of motor on bearing padastal both
bearings insulation resistance shall be checked by megger.
| Is This Answer Correct ? | 0 Yes | 0 No |
Please tell me the power flow from pmg to main rotor of an alternator (Including AVR unit)?
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
how to mention 5mw generator in kva ? gen voltage is 11kv
why we use dc motor instead of ac motor?
what is isolation Transformer?
defination of loads
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
what is the use of spherical metal balls attached on to the earth wire of transmission over head lines?
What is on line ups and off line ups?
some meggers have three terminals. wat is the real function of the earth terminal?
What is generator
why and how voltage sharing in transformer, during magnetic balance test ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)