ELCB is used to detect earth leakage fault. Once the phase
and neutral are connected in an ELCB, the current will flow
through phase and that much current will have to return
neutral so resultanr current is zero. Once there is a
ground fault in the load side, current from phase will
directly pass through earth and it will not return through
neutral through ELCB. That means once side current is going
and not returning and hence because of this difference in
current ELCB wil trip and it will safe guard the other
circuits from faulty loads. If the neutral is not grounded,
fault current will definitely high and that full fault
current will come back through ELCB, and there will be no
difference in current.
| Is This Answer Correct ? | 38 Yes | 13 No |
Answer / dayal varma
the main function of the ELCB is to trip the circuit when
ever the fault in earth ocuurs so it needs a ground
referance. other wise it will not work
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / chiss
Hi,all, i've got a problem with the understanding of ELCB,
may i know if only Red and yellow phase (2 wire of 3 phase)
connected to 4 pole ELCB? Does ELCB need a neutral to make
it work?
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / rayvandy
No, it doesnt need earth wire to be connected to elcb/rccb. But it is recommended to connect every electrical appliances in your house with earth wire/ground. When there is a leakage, the lccb will detect that current in the live wire is higher than current that returns to neutral wire through lccb. Because the two currents is not balance, lccb will cut off the electricity. For more info u can refer to this site: http://www.gcsescience.com/pme9.htm
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / mayuur
There is no need of connection to ground because there is two current pass which are passed in oppose direction so the flux in the coil has been nullyfied .
And if u connected n terminal into ground there the relay trip immediatly
| Is This Answer Correct ? | 2 Yes | 0 No |
Batteries. What is the difference between Lead and Nickel batteries ?
I want to know how to calculate the size of electricity cable in building?
0 Answers DR Engineering Services,
From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?
What is SNMP Card Monitoring in UPS???
What is the need of generator relay panel
What is the problem of internal failure in ship engine telegraph system norcontrol?
What is Class and accuracy in CTs? Types of Classes and important of Classes?
ALL HT /LT PANEL TEST? DISCRIPTION.
sir i had plane to do some project with the base of hopkinson test in AC supply its possible
6. A DC AMMETER HAS R=0.1 OHM & CURRENT RANGE IS 0-100 A IF THE RANGE IS TO BE EXTENDED TO 0-500 A THEN METER REQUIRES SHUNT RESISTANCE OF ..........
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
If auto trip is operated, can you close the breaker.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)