Between Star-Delta & Star-Star Power transformer which one
is efficent for Earth Fault?
Answers were Sorted based on User's Feedback
Answer / daher
star/star because in the case of line to earth faults the
zero curret IO in delta connection transformer has no path
to leave the close loop of three phases transformer
Is This Answer Correct ? | 17 Yes | 8 No |
Answer / nidhi
star delta .
because in star star connection solidal grounding should be
provided to ground third harmonics. in star delta whenever
afault will occur then it will circulate only in this delta
not go to the output
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sunil guru
Star - Star bcz.. it has a point at center which can be
used as a neutral or can be grounded,
but in case of star-delta there is no path for ground
return current during short circuit..an the circulating
current will flow inward itself and can damage the winding..
for any disagreement mail me at parmar20072008@yahoo.com
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / awais
Star star because for earth fault return path is required to complete the circuit so neutral grounded star connection is ideal for such type of fault detection..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / daher
star/star in case of line to ground short circuit in star -
delta transformer their is no path to I0 short circuit
current and it will turn inside the closed circuit of delta
connection
Is This Answer Correct ? | 1 Yes | 4 No |
how to wiring it with contactor and timer together
I am inpecting a 10kVA UPS what tests should i do and should i observe?
advantages of vvvf drives over non vvvf drives for EOT cranes
Either the Armoured Earthing strip of HT 3 core cable have to pass through CB CT or not , why ???
What is Hot reserves and spinning reserves?
What is an Isolation Transformer? Where it will use?
what is pmu
1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral and body earth & panel earth.
12 Answers HP, Malladi Drugs and Pharmaceuticals, Pearl Engineering, PL,
What kind of Neutral CT can be placed in 11/0.433KV transformer to be used and what are its specification?
what happens if you swap F1 and F2 connection in the exiter of the generator?
why near the transformers, the Jelly(small white colored rocks)are poured.and what are conditions for that?
In Delta connected capcitor bank, One bank failed due to some problem. Can we connect Open delta capacitor bank to 3 phase motor. The motor voltage rating is 6.6KV. IF yes what changes will happen?