Answer / daher
star/star because in the case of line to earth faults the
zero curret IO in delta connection transformer has no path
to leave the close loop of three phases transformer
| Is This Answer Correct ? | 17 Yes | 8 No |
Answer / nidhi
star delta .
because in star star connection solidal grounding should be
provided to ground third harmonics. in star delta whenever
afault will occur then it will circulate only in this delta
not go to the output
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sunil guru
Star - Star bcz.. it has a point at center which can be
used as a neutral or can be grounded,
but in case of star-delta there is no path for ground
return current during short circuit..an the circulating
current will flow inward itself and can damage the winding..
for any disagreement mail me at parmar20072008@yahoo.com
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / awais
Star star because for earth fault return path is required to complete the circuit so neutral grounded star connection is ideal for such type of fault detection..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / daher
star/star in case of line to ground short circuit in star -
delta transformer their is no path to I0 short circuit
current and it will turn inside the closed circuit of delta
connection
| Is This Answer Correct ? | 1 Yes | 4 No |
WHAT IS MEANT BY OVER EXCITATION IN GENERATOR TRANSFORMERS? DESCRIBE IT.
What is the make of breakers, transformers, generators? What are their capacities and ratings?
4 Answers Bharat Bijlee, GHPPL, Tata Motors,
What will be the full load current of 60KVA UPS. Suggest for this formula.
what's the use of cvt and wave trap in 400kv switch yard.......
What is working of Trip Ckt.Supervision Relay?
What is the problem if we connect a weak capacitor to the system? is that profitable or Loss?
Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required
9 Answers Emerson, Rajshree Sugars, Siemens,
How do apply electrical 'c'license......pls advice
what is the length of air terminal in lightening arrester system.
how pt is using
what is the maximum current carrying capacity of a 95 sqmm cupper under ground cable laid partialy in land and partialy in ground?
how to convert kw in to unit
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)