Between Star-Delta & Star-Star Power transformer which one
is efficent for Earth Fault?
Answers were Sorted based on User's Feedback
Answer / daher
star/star because in the case of line to earth faults the
zero curret IO in delta connection transformer has no path
to leave the close loop of three phases transformer
| Is This Answer Correct ? | 17 Yes | 8 No |
Answer / nidhi
star delta .
because in star star connection solidal grounding should be
provided to ground third harmonics. in star delta whenever
afault will occur then it will circulate only in this delta
not go to the output
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sunil guru
Star - Star bcz.. it has a point at center which can be
used as a neutral or can be grounded,
but in case of star-delta there is no path for ground
return current during short circuit..an the circulating
current will flow inward itself and can damage the winding..
for any disagreement mail me at parmar20072008@yahoo.com
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / awais
Star star because for earth fault return path is required to complete the circuit so neutral grounded star connection is ideal for such type of fault detection..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / daher
star/star in case of line to ground short circuit in star -
delta transformer their is no path to I0 short circuit
current and it will turn inside the closed circuit of delta
connection
| Is This Answer Correct ? | 1 Yes | 4 No |
what is the ohmic value of transformers
What is meant by Load Encroachment in OHL Feeder Protection?
I have a 25kVA three phase transformer on our property. Will this transformer be large enough to run a large home with swimming pool, spa, 2 off full size reverse cycle air conditioners to service a 100 square house (10,000 square feet or 930 square metres)and the general power consumption of this house without upgrading to a 63kVA transformer.
what is active power & reactive power?
is it ok to switch lights from a mcb instead of switches
How u can give the overload setting to any motor protection relay for a HT motors with formula and Example?
1. what is the power factor of a purely inductive load? (i) Zero (ii) Lagging (iii)Leading (iv) Unity 2. which type of transformer connection is preferred in case of power supply transformer? (i) Star/Star (ii) Delta/Delta (iii) Star/Delta (iv) Zig Zag/Star
why we don't use earthing as neutral?
Which Class insulation is prefered for the sandwich Busducts ? Why?
in an electronic tri vector meter when the current and voltage sequence changes ? what is the effect of phase sequence on recording of meter
What is the difference between grid and off- grid system??
what is SWA type of cable?????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)