which starter is used for synchronous motor
Answers were Sorted based on User's Feedback
Answer / moti rgpv
1-:STAR -DELTA STARTOR
2-:COUPLING WITH INDUCTION MOTOR AND REMOVE THE MOTOR
AFTER GETING 80% TO 90% OF SYNCHRONOUS SPEED
3-:USING DAMPER BARS
Is This Answer Correct ? | 48 Yes | 7 No |
Answer / mallikarjun
At first , the synchronous motor is coupled with induction
motor then the synchronous motor will run as a induction
motor and then the d.c supply is given to the field winding
of the synchronous motor ,the rotor will tends to magentic
locking with stator rotating field then that synchronous
motor wii run at synchronous speed
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / kesavulu
Generally Synchronous motors are not self starting motors.
A pony motor is required to rotate and D.C extitation is
also required.Liquified rotary starters are used
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / thiru
BUT IN THE OPTIONS THESE ARE NOT THERE
OPTIONS.
1)DOL 2)AUTO T/F
3)ANY ONE 4)NO ANS
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / moti rgpv
DOL is also correct BUT IT IS NOT WIDELY USE FOR LARGE
RATING FOR SYN. MOTOR.
SO IN OPCTION DOL IS WRITE
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ed
Across the line Starter.
with time delay relay or current sensing relay or
speed monitor relay to
energize the field when the motor is close to
synchronous speed
For above 600 volt motors, a Circuit Breaker can be
used instead of a starter.
Is This Answer Correct ? | 0 Yes | 0 No |
which type of motor using in drilling machine ? & who to produce very high torque in drilling machine?
1 Answers National Drilling Company,
why the efficiency of the dc machine is high ,when it is operated as a generator?
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
in science exhibition how lamp can blink when you clap near the lamp ? thank you
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
how brushed dc motor operating ?
what's transient & sub- transient reactance means?
if three phase supply is given to single phase transformer, what will happen?
Buchholz relay is used ………. a) protection T/F b) oil T/F c) Air core T/F
8 Answers Engineers India Limited,
what is the working of hydrent system.
what type of battery used for starting D.G?state its function?
In star delta Schematic can we connect OLR in delta circuit