how i calculate the size in mm of the LT 4 core cable for 100 HP inductive motor pump
Answer / narendra katakkar
100X.8=80KW
80KWX5=400A
400/3=133A per Phase
So for 133Amps 150mm2 cable is required
Is This Answer Correct ? | 0 Yes | 0 No |
how to check capacitor in general
What will be done if we open the secondary of CT on load??
In our generating power station we get electric shock in the battery bank, what will be the reason?
HOW TO CALCULATE THE VT SIZING?
Is it posssible to obtain the higher speed(3000rpm) for adiferentiallly cascaded induction motors(with 8 and 6 poles)
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?
what is the diffrence between voltage and current?
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
what is STUB protection in tranmission system and switch yard area?
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
An alternator is started without excitation then how much voltage it will produced at strating at full rpm??
what are the applications of PLC?