we have two 11/.433 kv. distribution Transformer rating as
1000 kva & 500 kva , i wants to run parallel both transformer.
both transformer impendence voltage is 5.24%, How can we run
both t/f, & how sharing the load
Answers were Sorted based on User's Feedback
Answer / kandasamy
Since both the trasformers are identical impedance , The
load sharing will be exactl equal OF TOTAL (LOAD)POWER.
Load sharing of transformer A= Power x(ZB/ZA+ZB).
Load sharing of transformer B= Power x(ZA/ZA+ZB).
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / aks
Both the trasformers will share the load equally.ie.50% by
each transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
As mentioned if the capacity, the vectror group ,
Impedance is equall you can connect both the transformet
in parrel just make sure that the Phase sequence for both
the transformer is same at the time of parallel & as the %
impedance is same the laad sharing will be equall.
| Is This Answer Correct ? | 0 Yes | 1 No |
Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
Why have to use copper cable for local isolator to motor ?
State Maximum Power Transfer theorem.
what is the use of sdf?
Sir, My doubt on cable sizing calculation, Load:74 KW calculated cable 1 run 50mm2. Now client asking us to reduce cable size by increasing runs. Sir, My question now when my mind strikes with 2 options 1) Divide load 74/2 = 36 and calculate cable for 36+36 making it 2 runs or 2) Simply i can divide 50mm2 /2 ie. 2 runs of 25mm2 Please suggest me sir
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
how to find out 3 phase complex power in per unit in unbalanced system?
Why using synchronising methed in DG's sets?
what is the use of current transformer in power transformer secondary side.?its connectyed in WTI
40 HP motor how many square mm size wire use for stator to motor & aluminium wire use ?
What are the advantages of autotransformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)