we have two 11/.433 kv. distribution Transformer rating as
1000 kva & 500 kva , i wants to run parallel both transformer.
both transformer impendence voltage is 5.24%, How can we run
both t/f, & how sharing the load
Answers were Sorted based on User's Feedback
Answer / kandasamy
Since both the trasformers are identical impedance , The
load sharing will be exactl equal OF TOTAL (LOAD)POWER.
Load sharing of transformer A= Power x(ZB/ZA+ZB).
Load sharing of transformer B= Power x(ZA/ZA+ZB).
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / aks
Both the trasformers will share the load equally.ie.50% by
each transformer.
Is This Answer Correct ? | 1 Yes | 0 No |
As mentioned if the capacity, the vectror group ,
Impedance is equall you can connect both the transformet
in parrel just make sure that the Phase sequence for both
the transformer is same at the time of parallel & as the %
impedance is same the laad sharing will be equall.
Is This Answer Correct ? | 0 Yes | 1 No |
Why the substation measure in KV but not in the power ratings of transformer.
What is P.F? Formula for calculating PF in HT side?
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
how could we know the size of cable by physical view?
0 Answers Havells, United Engineering,
In a ordinary plug can we hold the earth in hane and connect the circuit to supply?will we get a shock?
what is the difference between neutral and earth
what is the difference between the voltage of 5 volts capacitor and and 5volts battery?
mention the earthing system as per BIS?
why current transformer secondary is short circuited an what will happen if connect very high resistance acrossthe secondary side of current transformer?
How many types of earths are there?What is the maximum ohms of earthfit?
hello! sir i did three year of diploma in electrical (2007- 2010) and now i m a student of electrical engineering. sir can i apply for germany visa for study and part tome work over there?
why capacitors cant used in genset to maintain power factor..??