Answer / balram raturi
ciruit breaker operates on load but isolaters are operated
on no load or to isolate the healthy system.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ammajirao
The circuit breaker can operate in both ON load and OFF load
because quenching medium is available to extinguish the arc
but in case of isolator, it should operate in OFF load
only because of no quenching medium.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / koli60
c.b is protective equipment which is used to
protect tran. line in abnormal condition. we can operate
c.b. manualy as well as automaticaly .
while isolater is also protective equipment . but
isolater cant be operated automatically .
in normal condition isolater contacts are closed .
but c.b. is opened ........
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ankit
In the simplest form:
An ISOLATOR is a manual circuit breaker while Circuit
Breaker does this with the help of a relay.
Regarding the arc quenching medium, isolator too have air
as arc quenching medium.
And,
An iso. is an off-load device but a CB is onload.
| Is This Answer Correct ? | 4 Yes | 7 No |
In separately excited m/c,we excite the field by a dc source,what not with ac source?
what is the purpose of using battery in dg sets, please specify in details.
What is the concept of voltage & current its relation?
what is the eight bit unit?
What is the formula to find out cross sectional area of cable for certain current rating?
I know the Capacitor value- 12.5KVAR, voltage 440V gas filled, then what is the formula for calculate the microfarad value for this 12.5KVAR capacitor
can we use ac ameter as dc ameter with ct
Which types of Gases occure when mineral oil burnt
what is difference between megger & Contact resistance meter & its Application?
in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)