what is pf. how to calculate capacitor bank value to
maintain unity pf.
Answers were Sorted based on User's Feedback
Answer / nilesh kumar singh
Power Factor is defined as the ratio of Real power and
Apparent power.
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 101 Yes | 8 No |
Answer / rajendra singh
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 42 Yes | 8 No |
Answer / shivappa
to calculate desired capacitor value, the formula is
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 23 Yes | 14 No |
Answer / kim leang
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / midhun
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / fancy102
hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..
| Is This Answer Correct ? | 40 Yes | 36 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [√(1–(COSФ)^2)]/COSФ
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
TanФ= opposite/adjacent = S/P -----> S=P x(TanФ)
Pf=COSФ= adjacent/hypotenuse = P/Q ---->Q=P/COSФ
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COSФ)^2= P^2 + (P^2 x (TanФ)^2)
by divide P^2:
1/(COSФ)^2 = 1 + (TanФ)^2
by changing the both sides:
(TanФ)^2 = (1/(COSФ)^2) - 1
(TanФ)^2 = (1/(COSФ)^2) - ((COSФ)^2/(COSФ)^2)
by Taking the (1/(COSФ)^2) Common factor:
(TanФ)^2 = {1/(COSФ)^2)} x ( 1 - (COSФ)^2)
by taking the square root:
TanФ = [√(1–(COSФ)^2)]/COSФ
so that:
KVAR = KW x [√(1–(COSФ)^2)]/COSФ
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh
react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load
| Is This Answer Correct ? | 14 Yes | 11 No |
Answer / vekuva
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;
| Is This Answer Correct ? | 4 Yes | 1 No |
why HT voltage rating in multiple of 11
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
what is S.T?specify the range?
How power factor affect on bill explain with example.
What is Horan Gap Fuse? Where it is used?
how much power consumed by 1.5 ton capacity split A.C in 1 hour
what is the difference between synchoronous and alternator and induction motor and generator
wt wil happen if a 120kv line is grounded
operating Lt & HT voltages used in India?
1000kva = how much kvar
Whatis the procedure for getting Electrical (light) licence while Iam a diploma holder in electrical Engg . I Compleated my one yr Apprentice training & worked as a junior engineer (ele) for 2 yr(contract basis).
What is the operational principle of direct current current transformer and direct current potential transformer?if possible plz reply with ckt. diagram.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)