what are the difference between protection class CT and
Class PS CT

Answers were Sorted based on User's Feedback



what are the difference between protection class CT and Class PS CT..

Answer / siddharth agasti

class ps ct is a protection class ct.it is used for
differtial proction,distance proction.

Is This Answer Correct ?    47 Yes 4 No

what are the difference between protection class CT and Class PS CT..

Answer / chetan joshi

Protection class CT are 5 p10 and 5 p 20 and PS class ct
are used where neutral point is available such that star
conneccted secondary of Transformer and alternator ,it is
used for differential protection.

Is This Answer Correct ?    25 Yes 9 No

what are the difference between protection class CT and Class PS CT..

Answer / shivaji mangalagiri

all the protection cts like over current
relay and earth fault relay of transformer,Alternator and
HT motors are having core 1 and core 2 options. CLASS PS
type is used only for differential protection purpose of
transformer,Alternator and
HT motors only. and this type of cts are available only in
PAIR SCHEME (PS) AND their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.

Is This Answer Correct ?    18 Yes 4 No

what are the difference between protection class CT and Class PS CT..

Answer / s.rajasekar

the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections ( REF,DIFF,DISTANCE )

Is This Answer Correct ?    9 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / patel indukumar

Protection class is ued in protection like over current
relay and earth fault relay of transformer,Alternator and
HT motor.PS class is used in DIfferential protection like
transformer,Alternator and HT motor.

Is This Answer Correct ?    13 Yes 6 No

what are the difference between protection class CT and Class PS CT..

Answer / manoj

Both Protection class and class PS CTs are used in
protection circuits only. As someone mentioned earlier,
class PS CTs are special CTs used in all types of
Differential Protetion scemes. they generally come in pairs
and they are special in sense their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.

Is This Answer Correct ?    8 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / satheesh

the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections (DIFF,DISTANCE )

Is This Answer Correct ?    4 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / mauhammad yasir abdul-rub

The Difference Between protection class and metering class
is mainly of saturation, the saturation values of protection
class is higher as when fault occur protection CT must not
get saturated as high current flows and metering CT can be
saturated as when fault occur metering is not necessary,
accuracy is also a factor but not the main factor

Is This Answer Correct ?    8 Yes 6 No

what are the difference between protection class CT and Class PS CT..

Answer / selvam.s

Protection CT:

this type of CT can be used for protect the breakers.

5P10,5P15 & 5P20 are called protection current transformer

1) 5 means accuracy of sensing fault current
2) 'P ' means "protection"
3) 10,15 & 20 means ( no.of times ( 10,15 &20 ) X actual
current rating of breakers .

PS CT:

PS means protection special current transformer.

this type CT can be used for differential protection in
transformer & in alternator.

Is This Answer Correct ?    2 Yes 0 No

what are the difference between protection class CT and Class PS CT..

Answer / r.suryamuthuraman

if any fault occurs core needs to saturated for protection
of ct.because ct secondary ckt will goes to relay current
coil .secondary ckt of ct will having resistance and
current.to avoid saturation want to decrease the burden of
ct.ps means special protection having high accuracy than
other class

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What is the name of the winding from which the supply is taken for load connections?

0 Answers  


what are the differance between neutral and earthing?

3 Answers  


THE ROTIO OF VOLTAGE AND CURRENT IN A CLOSED CIRCUIT

12 Answers   APGenco, Constant, Lanco,


why DC current not used in Transformer action?

17 Answers   Engineers India Limited,


transformer cooling fan kharab ho jaye to 1-off kar dena chahiye 2-load kum kar dena chahiye 3-koi frrk nhi padta 4-sub galat hai. choose right option

2 Answers   PGVCL Paschim Gujarat Vij Company Limited,






How can I calculate the require lumen of a room. If I use Tube Light (40 W), Or 100 W incandescent lamp. Please give detail answer.

1 Answers  


Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?

6 Answers  


how can alculate the apfc panel rating?

3 Answers  


What is the basic of DTH.

0 Answers   IOCL,


40 HP motor how many square mm size wire use for stator to motor & aluminium wire use ?

1 Answers   SSPL,


What is Nominal voltage?

3 Answers   Bhel, Equate,


what is the difference between transformer and amplifier ??

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)