what is sevice settings for mccb?How can be it setted?
Answer / mukund
it depend which mccb you have most hase thermal and
megnetic ttrip setting for thermal you cand set may 110 to
120 % of full load amp. and megnetic 3 to 10 time of FLA go
with less time suppose 3 time if mccb trip when load
connected increase little higher
Is This Answer Correct ? | 1 Yes | 0 No |
Your B.tech marks is being given in CGPA grade. How is it calculated?
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
Pls tell me what is the exact current conducting capacity of copper and aluminium cables?how much capacity of cables need to 90kw induction motor&how?
could any one explain me what power factor and where it is use ful
wat is the criteria we use the diff. relay ?
a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
how to calculate single phase motor efficiency ?
Why earthing is required, and what effect in earthing result is more than 5 ohm and less than 5 or equal to 0 ohm
what is need of air gap in expansion section in busbar?
what is power factor?
8 Answers Adani, Blue Star, Power Control,
what is our body resistance value?
why the transformer primary terminal indicated by u,v,w.to technical reason