what are the difference between protection class CT and
Class PS CT
Answer Posted / mauhammad yasir abdul-rub
The Difference Between protection class and metering class
is mainly of saturation, the saturation values of protection
class is higher as when fault occur protection CT must not
get saturated as high current flows and metering CT can be
saturated as when fault occur metering is not necessary,
accuracy is also a factor but not the main factor
| Is This Answer Correct ? | 8 Yes | 6 No |
Post New Answer View All Answers
i have attended the interview on 4th June,08 at Kolkata in IOCL, can anybody tell me what is its result
What are the internal and external faults?
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
What is dielectric loss?
If the rated speed of a d.c. Shunt motor is1440 r.p.m, which method of speed control would you suggested to obtain a speed of 1500 r.p.m?
what is accuracy ? in any meters , coils accuracy . how can u defined that ?
WHAT IS IEC? & WHAT IS BENEFIT TO PRODUCT FROM IEC?
What information we need to prepare relay coordination chart
what is the need of starter in tube light and what type of starter is used in that?
how to calculate energy of 3-phase motor?
What is superposition theorem?
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
How much no load current of synchronous motor
how to decide choke rating for drive?