what are the difference between protection class CT and
Class PS CT
Answer Posted / shivaji mangalagiri
all the protection cts like over current
relay and earth fault relay of transformer,Alternator and
HT motors are having core 1 and core 2 options. CLASS PS
type is used only for differential protection purpose of
transformer,Alternator and
HT motors only. and this type of cts are available only in
PAIR SCHEME (PS) AND their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.
| Is This Answer Correct ? | 18 Yes | 4 No |
Post New Answer View All Answers
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
wht is embedded systems? what is new inthis field?
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
What are the uses of stepper motor?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
What is the main cause of magnetism?
List examples of current sources?
What is the difference between Encoder and Resolver?
what is p.s impedance measurement test in earthing transformer?
what is the difference between gas group b and gas group c electrical equipment construction wise?
In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases
What does the a,b,c of 95a,95b,95c relays denotes?
HOW DOES THE ELECTRONIC ENERGY METER WORKS?
Explain few advantages of electric traction system?
why normally Generator rating are between 11Kv to 22Kv?