what is the suitable voltage of transmission line to
transmit 10000w power through 250 km.
(a)11kv
(b)33kv
(c)66kv
(d)132kv
]and please tell me whats the logic behind it
Answers were Sorted based on User's Feedback
Answer / sunny maurya
I WILL SUGEST U TO PREFFER 66 kV LINES BECAUSE THE POWER TO BE TRANSMITTED IS NOT MUCH ,IS IN kW ONLY.logic behind this is that line losses r less at higher voltage, but u will think why not to use 132 kV lines ,It is because at higher voltage insulation cost increases,and cost of equipments as well.
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / nilesh chitalia
I prefare 132 KV for Transmit 10 KW because of high
distance, at high distance of transmission there is a high
loss of power in low voltage, otherwise the the diameter of
the conductor should be high and ultimately the cost of
conductor shall be high. So, It is better to transmit at
250 km, 132 KV is better.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / m thiyagarajan
Higher the voltage lower the voltage drop V=IR so 132kv
transmission is better
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / paridhi jain
132 kv because if high voltage is transmitted den volume of
conductor material req will be lesss n also losses will be less
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / paridhi jain
132 kv because if high voltage is transmitted den volume of
conductor material req will be lesss n also losses will be less
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / rod
The higher the voltage the greater the distance as the
current is less but the power is the same. For very long
distances DC at very high voltage is used.
| Is This Answer Correct ? | 1 Yes | 9 No |
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,
what is an oscillator?
What is percent age of scrap of wires as per IE Rule Clause No in wiring for House and Industrial wiring ?
Why saturation region slowly shifted in the left side?
what type circuit breaker is suitable for connecting 1000A load VCb,Mccb?
what is sustainable current of any conductors . a bare busbar or pvc cable has different sustainable current .
In transformers Which type of connection is preferred for harmonics to be minimum. primary : secondary star without neutral:open delta star with neutral :open delta star without neutral: delta star with neutral : delta explain why
pls send me some question and answer for rrb railway interviw related 2010
What is the physical significance of phase.. i.e. what is exactly the meaning in layman's language.. 1 phase, 3 phase etc ???
how the inductor will work on dc supply?whether it will work or not?
What percentage netural current is in netural depend upon the phase current
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)