Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE
IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND
TAKING OUTPUT FROM PRIMARY?

Answers were Sorted based on User's Feedback



CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / sadananda

Dear Mr Akialok,

I think, the answer what you have given is not completely
right.As the VA ratting is not going to change in the
transformer, the max current in primmary & secondary will
remain same in whatever way you use.
For example: For 1 KVA 220 V to 110 V trafo, Max primary
current I1=1000/220 = 4.55 A & Max Seconday current
I2=1000/110 = 9.09 A.
So even if you reverse the source voltage, in any way you
can not use for more power.
Please reply for clarification.
Sadananda

Is This Answer Correct ?    27 Yes 1 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / akialok

during the design of power transformer,or any distribution
tfr the load current is taken into account ,and the windings
of the secondary side are accordingly designed that is the
load currents it can sustain ,insulation and cooling system
are taken into consideration...
suppose in your designing u r designed the windings to
sustain a 30 amp load current while reversing the windings
and taking the out put from primary as u stated, the load
current will be decreased at the 415 voltage side and the
current in the 220 voltage ll be increased to a factor of
transformation ratio as it has to work in same power..so the
windings of the 220 side may burnt out..if its not capable
of sustaining the increased current.

Is This Answer Correct ?    25 Yes 6 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / guest

yes certainly be used as out put from secondary

Is This Answer Correct ?    19 Yes 4 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / deepakindi1

sunil r u an ELECTRICAL ENGINEER? WHAT AN AMAZING ANSWER

Is This Answer Correct ?    22 Yes 7 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / vissu73

ideally we can use. but practically there are limitations to
use. as the reasons are given in answer 2

Is This Answer Correct ?    13 Yes 3 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / imran

I THINK ANSWER # 9 IS ABSOLUTELY CORRECT

Is This Answer Correct ?    12 Yes 2 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / kanth

i agree with 9 th answer

Is This Answer Correct ?    5 Yes 0 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / manoj jha

We can use the step-down tansformer as step-up transformer.
Secondary of the Transformer can be used as Primary. I am
using it since last five years. I have no problem. Our
Transformer was Step-Down , 2400/440V which was ordered by
mistake. Actually we were in need of 440/2400V. So we
connected the same Step down transformer as step-up
transformer and it's working pefect.

Is This Answer Correct ?    10 Yes 6 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / elangovan t

Definitely we can use as long as we adhere to the kva rating
of the transformer.

Is This Answer Correct ?    6 Yes 2 No

CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200..

Answer / avan

mr Manoj. are u saying currectly.
if yes then i agree with u

Is This Answer Correct ?    6 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

line diagram for mcb , mccb , rccb .

1 Answers  


To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?

0 Answers  


as per BIS supply voltage in India is ......

9 Answers  


I AM COMPLETED DIPLOMA IN E.E.E. AS WELL AS B.TECH IN ANDHARPRADESH.. HOW I THE Certificate of competency as Electrical Supervisor.

1 Answers  


If we tell 60 sq.mm. 3-1/2 core cable,then what does it mean ? 1) Each core section in the whole cable is of 60 sq. mm. 2) The whole cable is of 60 sq. mm. which is sub-divided into 3-1/2 core.

3 Answers   Cura HealthCare,


can any one tell me the formula to select the thickness of wire selection according to ampere rating

2 Answers  


seromechanism

4 Answers   Bhel,


what is the size of cable for 15kw motor and 85 meter cable length using with vfd

0 Answers  


Draw a circuit diagram in which if button is open we can use socket and bulb as a series test circit and if button is close than simple we can use socket as any load purpose.

0 Answers  


If the positive terminal of batteries in 125 v dc system is connected to earth what will happen ?

4 Answers  


HOW TO CALICULATE THE LEAD ACID BATTERY AH AND HOW TO FIND THE 1.2KVA UPS BACKUP @ 1000WATTS LOAD?

2 Answers  


why the voltage and current in a long transmission line are called travelling wave?

0 Answers   UIU,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)