For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / sharafuddeen
AS PER IEEE 400.1 ,THE DC TEST VOLTAGE SHOULD BE 100KV FOR
A 35 KV CABLES.AND THERE IS NO A PARTICULAR FORMULA TO
CALCULATE THE TEST VOLTAGE.IT SHOULD BE AS PER THE
STANDARDS AS PER WHICH THE CABLES MANUFACURED.
Is This Answer Correct ? | 9 Yes | 25 No |
Answer / ganesh
AC High voltage Insulation test : 132KV for 5 Minute.
IR test to be conducted before and after the AC high
voltage insulation test - 5KV DC for one Minute
Is This Answer Correct ? | 8 Yes | 28 No |
we are cheking only lekage current of cable
applicable value of voltage of 33 is should be 27kv dc
Is This Answer Correct ? | 7 Yes | 28 No |
Answer / ttrrail
AS HI POT TEST IS CONDUCTED IN DC, 25 KV SHOULD APPLY TO
THE 33 KV CABLE
BECAUSE
33KV X 0.707(RMS VALUE TO AVG VALUE CONVERSION) = 25KV(OPPR)
Is This Answer Correct ? | 28 Yes | 89 No |
why one pin of plug pin is longer than other two? In some mobile chargers one pin is made not conducting .Why?
what is the principle of generator, motor, and transformer and explain the definiton of flemings left hand rule , right hand rule and ohms law
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
Enlists the applications of sampled data systems?
if the supply voltage increased by N times, the x-section of conductor will be.........
2 Answers APGenco, Electrical Tech, Ericsson, IES, Thirumalai Chemicals,
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
why the transformer ratings in kva
what is meant by dielectric breakdown ? where we using HV test kit & what purpose?
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
Why wind turbines wheels rotate constantly
If excitation will increase, then what will be the effect on power factor? Will it decrease or increase?
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately