sir , what happen if we decrease ( approx 3 inch ) the
lenth of shaft in 110KW Induction , three phase motor.
actually a 110KW motor is couppled with star couplling to
120TR compressor. When we doing maintenance in compressor
it is required to skid the motor backword and resulting dis-
alightnment . so we want to change the tyre coupling in
place of existing coupling. so it is required to cut off
the rotor aprox 3 inch form driving side.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Cutting shaft short will not affect anything including
dynamic balance
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sunil kumar kr
While it can be generally stated that cutting the shaft will nor result any problem, this matter is definitely to be taken up with the manufactures. As the shaft size is reduced and new coupling is introduced, it is likely to affect the maximum torque that can be transmitted to the compressor.
| Is This Answer Correct ? | 0 Yes | 0 No |
i want all question & answers of the written exam
1 Answers Essar, L&T, MES, RRB,
why the vector group of excitation transformer is YD5(150 deg)how is this factor decided.
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
what is the actual difference betwen constructional details and constructional features?
What should be cable size for 75KVA 380/220 3ph transformer
what are the protection relays for trasformer
my bachelors was done with EEE now i got admit in NU with CS as course. how to answer this qns 1) why u choose cs? 2) why u changed from eee to cs
what is the function of short circuit maintenance ct and droop ct.
when we connect the capacitor banks in series with the circuit?
what is Ith current?
what is the difference between the 94 lockout relay and 86 lock out relay. I have noticed that the 94 lockout relay is activated when the distance realy is activated and 86 is activated when the 87T differential is activated. but why can't the same lockouts be used for both the protection schemes
why the rating of dc generator is in kw where as rating of alternator is in kva?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)