how we can select MCB ratings according to Voltages, Curves.
Answers were Sorted based on User's Feedback
1.We can select the MCB's acoording to Voltage is simple,if
we want 230V,select single pole MCb's else want 415V select
3 pole MCB's.
2.We can select the MCB's according to to Curves is also
simple,there are several types of curvature available..
there are,
B type: react quickly overload i.e 3-4.5 times of full load
current
Type C: react more slowly,these are recommended for
inductive with high inrush currents like fluorescent lamp.5-
10 times of Ifl
Type D: 10-20times of Ifl,recommended for very high inrush
current.
Type K: 8-12 times of full load I,recommended for cable
protection to be provided which include
motors,capacitors,and transformers
Type S: 13-17 times of Ifl,recommended for protection of
control Transformer,
Type Z:
Is This Answer Correct ? | 31 Yes | 2 No |
Answer / kundan kumar
MCB rating depends on voltage as well as load, so first of
all we will have an idea about load which will connected to
MCB.
Is This Answer Correct ? | 10 Yes | 2 No |
how we can improve P.F. by using capacitors ?
what is the difference between gas group b and gas group c electrical equipment construction wise?
what are the materials used in HRC fuse
what is the difference between earth leakage and earth fault?
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
How To increase Knowledge Of boliler regarding To Only Electrical Field..
how many earthing required for ups, what should be the earth voltages
how to caculate cable size for diff types of loads? if anyone know the calculating procedure please tell me
What are the causes of eddy current losses?
What should the transformer connection of a 11/220 kV step up and 66/11 kV step down transformer ?
how the CT and PT is connected in the circuit during testing of transformer explain with diagram
In LRS how much water PH value maintain for good operation of motor?