Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
Answers were Sorted based on User's Feedback
Answer / raul
Theoritically it is like dat only dat the frequency n voltage of the incoming machine must match the grid frequency n voltage for proper synch, but practically it is kept slightly higher in order to reduce the impact on speed governor n automatic voltage regulator bcoz as the grid pulls d generator into synchronism, there is sudden load applied on d generator due to which there is a dip in both frequency n voltage of d generator which is 2 b corrected by the speed governor by opening d turbine valve more n more steam enters into turbine which corrects d dip in frequency n on d other hand d AVR corrects d dip in voltage by giving d signal 2 d pilot exciter to give more excitation 2 d rotor field winding of d generator.
I hope d concept is now clear 2 u......
| Is This Answer Correct ? | 9 Yes | 3 No |
In theory the frequency and voltage should match exactly.
In practice the incoming generator voltage and frequency
should be slightly hogher than the grid.
This is to prevent the set from tripping on reverse power
or kva. The incoming generator will pick up some load
straight away so the frequncy and voltage matches the grid.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / raul
Please read some quality books first b4 answering such questions......... but still thnx for some brainstorming
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / b goutham
Actually the condition for synchronization is voltage and frequency of incoming generator should be equal to the grid otherwise there will dead short cicuit...and also large currents flows through the incoming alternator which may damage the winding of the alternator.....so the voltage and frequency should be the same...
| Is This Answer Correct ? | 0 Yes | 6 No |
Which has more losses, AC or DC??
What is BusBar integrity test and how it is conducted?
Why transformer called by KVA?
Which test will be more severe for VCB?
WHAT IS THE NECESSITY OF GIVING PARTICULAR COLOURS FOR 3 PHASE TRANSFORMERS.....
why the secondary winding of the transformer is not open circuited ?
5 Answers Nepal Electricity Authority, Torrent Pharma,
What is the different types of cable & current capacity of cable
I am getting diesel genset 62 kv for my house In addition there are 6 meters of 11kv for the house Lift also being installed for house plot sise 200sq yds total 4 + 2 foloors I want to know how much earthing required how deep it should be
What is the function of interposing current transformer?
What is proximeter? where it is used and why?
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
why ups rating in kva? and why ups are in parellel?.why isolation transformer is used in ups?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)