Answer / ravi
The neutral conductor is a current carrying conductor,
effectively the power return for each of the hot conductors
in a circuit.
The ground conductor is not intended to pass current except
in a fault condition, and then only long enough to trip the
protective device. It is typically connected to the frame
of an appliance, so that if a hot conductor were to break
inside the appliance and touch the frame, the protective
device would trip, instead of the frame becoming hot - an
electrocution hazard.
Neutral and Ground are connected together at the
distribution panel, but since that is a single point, there
should still be no current on ground.
In the event that a current path to ground were created,
such as touching a hot pin while touching a faucet, an
electrocution could result unless there is a GFCI (Ground
Fault Current Interrupter) in the circuit. This device
checks that the current on the neutral return exactly
matches the current on the hot supply, with imbalance
representing a ground fault. (Kirchoff's Current Law: The
current at all points in a loop is the same, or the sum of
the currents at a node is zero.)
Is This Answer Correct ? | 1 Yes | 2 No |
how many BUSBAR is in electrical system?
Which system is best for industries 3ph 3w or 3ph 4w?
Igfet is a
how we calculate the dick for a pole?
use of PIR in ehv breaker
Operation carried out in thermal power stations?
onan full form
WHAT IS THE MINIMUM IR VALUE FOR CABLE CHARGING
What is surger vector in 33Kv transmission feeder? We have AC power generator of 8MW which is paralleled with 33Kv EB grid. Some times our HT breaker gets trip off due to surge vector problem. How to over come it? Is there any device to observe the surge and avoid tripping?
what is the difference between the alternator used in hydro and thermal power plants??
why there is a humming noise in transformer
HOW TO IDENTIFY THE RELAYS WHICH APPLICATION IN WHICH RELAY USING?