My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor
Answers were Sorted based on User's Feedback
Answer / abdul rahman
Required capacitor KVAR :- KW X [tan cos (inverse(power factor old = 0.8)))-tan cos (inverse (power factor new = 0.9]
KVAR :- 15(TAN(C0S INVERSE (0.8)-TAN(COS(INVERSE (0.9))
= 15(TAN 36.86-TAN 25.84)
= 15(.75-.48)
= 15(.265)
= 4 KVAR
| Is This Answer Correct ? | 6 Yes | 0 No |
Using formula KVA^2= KW^2 + KVAr^2 ,find the values KVAr at 0.8 and 0.9 pfs. The difference is the required KVAr of the capacitor
| Is This Answer Correct ? | 4 Yes | 5 No |
What is limitedly stable system?
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
why in transformers voltage given is in the multiple of 11
Detailed working of a diesel generator set ?
1 Answers Airtel, Honda, Kirloskar,
If I want to buy a new Xformer for my plant what are the main parameter will I need to check?
How many earthings are required for motors?
What happens instead of using 3 phase, if we give loop of single phase to all three phases ??
How to calculate battery back up time for a 400 AH battery bank installed in telecom shelter for a load of 20 Amps and time taken to fully charge this battery bank?
Wind mill
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
What is meant by Low Resistance Cable and High Resistance Cable.
why there is a high voltage line in multiplication of 11?i.e.- -66kv,11,kv,22kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)