I have two power supply.a)govt. power b)Captive power.3
phase load connected inside factory.when source change govt.
source to captive some motor rotate reverse. Is phase
sequence changes when if off & on?If I off generator & on it
again is it possible to get changed phase sequence??
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The phase sequence does not change if you switch on and off
the captive power. Interchange two leads of the captive power.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ganesh.a
no phase change will accur if u turn it off nad on again.check
the polarity of captive power
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ali raza
yas u can change the phase sequence from main supply any one (govt. or captive) then your motor rotate in one direction at both supply in our plant also same condetion happend then we change the phase sequencein generator terminal
| Is This Answer Correct ? | 0 Yes | 1 No |
what happens when power factor leads or lags to electical or home appliances
what is the sludge current
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
why the rating of a transformer in kva not in kw.
how to identify small motor and generator?
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
how caculate the pump head to maintain perticuler pressure of water and what would be the motor size in hp for the same?
what is F.A.P in fire alarming system?
state the disadvantages of carbon filament???
What shocks us , Current or voltage?
How to check the efficiency of the generator , air compressors.
i have ht transformer of 142 kva with air cooled facility,having secondary voltage 7850volt, and secondary connected full way bridge rectifier .i faced the problem repeatedly that transformer one coil and rectifier diode of two phase was burnt two times. i checked all the secondary ckt. no any short ckt found,then what will be the cause side
2 Answers Modern Terry Towels,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)