How can we calculate the Rating of DG Set for a 4 kw motor?
Answers were Sorted based on User's Feedback
kw 4
hp 5.434782609
amps 7
DG selection is grater 3to 4 times
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / seeni labeer
Motor Rating = 4kW
Useually generator ratings are in KVA
KVA=KW / PF
KVA=4 / 0.8 (Useual pratice power factor = 0.8)
KVA=5
The required rating of DG for 5KVA on 4kW Motor
| Is This Answer Correct ? | 0 Yes | 0 No |
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
0 Answers Apotex, Periyar Chemicals,
wath is this mining of bts
What is the principle of Excitation.
What is Black-out and Brown-out situation in the context of voltage stability in power system?
What is PQA???Applications........
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
Motor and transformer working with same principle so why motor rotates while transformer not?
Can we use Motor protection CB while we use the VFD for Speed control?? if not means please tell the reason!!!
is it possible to run the any motor when winding grounded? how?
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?
What do you mean by the zone of protection?
How to Convert horsepower to kva? what is the three phase formula? email me if u know thanks Rehan smileavail@msn.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)