Answer / awdhesh
When neutral disconeted bulb are in series so ckt current is same but voltage drop is diffrent.vlt drop is propesanl to R so 100W lamp R is more with respect to 200W. 100 W lamp fuse first.
| Is This Answer Correct ? | 37 Yes | 5 No |
Answer / velmurugan
100W lamp will fail first, Although the voltage across 100 w
lamp will be higher (293V), but it will fail because of
effective current (0.489A) which is more than the 100 w
lamp normal current (0.4A). Increase in current cause more
heat and heating element will fail.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / harsh
It might be .... the Phase issue ...
Phase R is Generally 120 angle ahead of phase Y...
Lets suppose A complax situation here..
We are now going to add an another Load of 300w in phase B
With same voltage drop..
At that time also 100 watt bulb would b fuse First...
| Is This Answer Correct ? | 0 Yes | 7 No |
why transformer rating in kva ?
what is star&delta connections?
In a closed circuit if two 5volt power supplier are connected in parrel what is the current direction in tihs circuit?
ROC converges if poles and zeros lie inside a. Origion b. Z=1
why so voltage is same in parallel circuits and current is same in series ckt?
What is Harmonics & what are its efect & which harmonic is dangerous
How the electric train gets the supply of electricity? What is the return path of the current?
Generally the incandescent lamps in bathrooms fuse due to high voltage at night.What is the simple solution of this problem?
What is essential to prove safe isolation of electrical circuit?
from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?
why ac supply neutral should earth not in dc (-)
what should be the value of proper neutral earthing resistance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)