What is the rating of your capacitor bank at your company.
Answers were Sorted based on User's Feedback
Answer / ushankar198931@gmail.com
2500Kva transfermer use 1000kvar capacitor
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / vijay kumawat
if your power factor is suppose 0.75, and you have to improve your pf to unity then find the inverse cos of 0.75, then find the tan(cos^-1(0.75)).
then find the value you have to improve the pf suppose you have to maintain to unity then, cos^-1(1) then find the tan (cos^-1(1)).
the find the [tan (cos^-1(1)) - tan(cos^-1(0.75))] * kw of motor
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / engr.shahbul
2.5, 5,7.5, 10, 12.5, 15, 20, 25,50, 100KVAR
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sp singh
To maintain p.f. we use capacitor bank generally.for LV system we use APFC and in HV System we use bus capacitor.In industries we generally use equipments having lagging pf like motors, lighting chokes etc ,capacitors supplies reactive power to the system and improve power factor
Is This Answer Correct ? | 0 Yes | 0 No |
hi ravi,
we are using 660KVA APFC Panel
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / akshay magar
capacitor bank rating of our company means how to calculate the capacity of capacitor of ur company and its important for improving powet factor of company.
Is This Answer Correct ? | 0 Yes | 0 No |
The size of your capacitor bank will depend upon your load, existing power factor and your required power factor.
Is This Answer Correct ? | 0 Yes | 0 No |
what is creepage distance
why tertiary winding is used in transformer with diagram?
Is phase preventer require when overload relay is there
how to check capacitor in general
pls tell us AC plant are how do work and parts name with picture
Three way plug point is there ,in that plug why we need earth pin is bigger than compare with phase and nutral pins?
How do we check transformer losses and what are the ways to minimise it.
What happened If 3phase supply connected to slip ring side of slipring induction motor ?
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
Define super node?
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.