what is the maximum Load capasity in LV-Panel,MDB,SMDB &
Final DB'S in Electrical disribution system?
Answers were Sorted based on User's Feedback
The MDB Maximum load depends on the Transformer,it is not
constant for the max load,if you want make load calculation
first you consider load downstream to upstream,please
following the steps...
*Calculate the Area(sqf or sqm)
*Calculate the load(lighting =1.5w/sqf,power=1w/sqf etc....)
*calculate the floor wise and get total load
*Applying the d.f and L.f and find the trf rating
*now you can design the MDB ,SMDB and FDB
| Is This Answer Correct ? | 34 Yes | 12 No |
In Generator How suction compression power and exhaust works ?
explain LED lamps?
what happens when current(ac or dc)flowing through a boucket of water?please describe it.
What is VFD, and how its work
Why Capacitor & ignator used in MH lamp
Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core
one kva is equal to how much amps?
How do i calculate sizing of transformer on didstrubution load for high rise building.What should be MVA Rating of MV Panel feding by 122 kv.
how to select fuse rating for a 3-phase motor ???
WHAT IS THE TECHNICAL SPECIFICATION OF C CURVE & D CURVE LEGRAND MAKE MCB
STATE AND EXPLAIN SUPER POSITION THEOREM.
what is the mean of short circuuit current ( for ex. 50KA)?
2 Answers Weltech Engineering,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)