How to select Main CB Rating for 187 KW Load?
Answers were Sorted based on User's Feedback
Answer / abdulsubur
Total load =187kw
p=root3*vicosphi
i=p/root3v*cosphi
we get aprorximately 400
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ramaraj.g
Selecting main CB rating first.
187KW / votages LL
187000/400
467.5 amps this type current rating is not in market
so we will go to next rating 600 Amps
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / abdulsubur
P= Root3*vicosphi
calculate i from this equation apploximately
we can use 400A ircuit Breaker
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rajendran
Apart from the nominal operating current we have to
consider the following factors also
1) Capacity of the source
2) Fault lvel of the system
3) Breaaking capacity of the breakeer required based on the
fault level obtained..
4) Space avilable
5) cost requirements
6) Method of controls in the breaker
7) Protection facilties avilable....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / bala
Selecting main cb rating depends on the type of load if it
is combination of small loads (upto 10kw) 400amps mccb is
enough.
1. if it is one motor load. first we have consider what
type of starter we are going to use. in case of star delta
starter select 600amps mccb. in case of VFD and softstarter
400amps mccb is enough.
| Is This Answer Correct ? | 4 Yes | 3 No |
is there any concept of armature reaction in Induction motor?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
why receiving end voltage increases in a system when capacitive load is added
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
salam&hi, i need to know about how can i calculate an enough current for the new building before i submit it to the suppliers
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
What is class X ct? What rare its uses?
Due to velocity saturation, MOSFET reaches saturation a.Before Pinch off b. After pinch off c. At Q point d. Before Q point e. After Q point
What will be the total current for 300kva UPS if it runs on 40 to 45 percent load. Is there any formula for to calculate the exact load.
What is the ladder circuit?
1 Answers Mitharg Information Systems,
Why Neutral Earthing pits and body earthing is interconnected
Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)