Answer / sisir kumar singh
the general principle of installing capacitor bank is
take 35% of the connected load.and in a capacitor bank put 12 -15% as a fixed capacitor.
suppose your connected load is 1000 kw then the capacitor bank size will be 350 kvar and the fixed capacitor will be12-15% of 350 kvar that is 42 -53 kvar
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amanpreet singh
240V to 2490V and size of 2.5kvar to 1000kvar
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / manjunath.m
Maximum we can connect the capacitor bank 40% of the
contract demend.
EX: our Bescom contract demand is 1000 kvar.
we can connect up to 400kvar capacitor bank panel.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / md.nur nabi hossain
for 11kv , capacitor bank will be1500kvar.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / suresh kumar
The capacitor maintained current load and the power ffactor 0.91 to 0.99 is correct values of capacitors in ac supply and DG set of pf is 0.85
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shubhanshu
in my company we have installed two capacitor banks of 3.242 MVAR to improve the power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Difference between SFU & FSU with advantantages & drawback?
What are the neccessary safety arrangements before commissioning of HV substation?
How to address the servo drive for motor
if we are using ACB in a panel the how much clearance do we need in panel room.
how to converate kva to kw ?
how to calculate cable size in transformer, distribution side?
What will happen when we will connect lamp in between phase and earth.
CTs Ratio
how you will decide the distance between the power transformer and its fencing
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
why Power transmssion voltages are as 11kV,33kV,66kV,220kV and so on only?
Why a transformer is known as a static device?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)