Answer / nitish katoch
no we can we can only calibrate measuring devices..its
calibration is only depend upon its design
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / velu
Actuator can be calibrated. for example Pneumatic Actuators
are used in control valves. we have to calibrate the
Actuator as per name plate depend on the actuator size and capacity(call us bench set) for proper opening
and closure of the valve.
Is This Answer Correct ? | 4 Yes | 0 No |
Actuator can be calibrated. for example Pneumatic Actuators
are used in control valves. we have to calibrate the
Actuator between 3-15psi pressure range, for proper opening
and closure of the valve.
there is nothing saying whether field
devices alone can be calibrated. All process control as well
as sensing devices should be calibrated periodically.
Is This Answer Correct ? | 4 Yes | 3 No |
You cant calibrate an actuator, you can just do setting.(
setting means better performance and more accurate ).
But calibration is the process of measuring the actual
performance of an instrument-under-test using lab
instruments ( or we can do this in the field ) that in
turn have significantly better performance than the
instrument-under-test. The measured performance is then
compared to published data sheet specifications. If observe
the instrument to be out-of-specification, instrument must
adjust and re-test .( for example we can do calibration for
a thermocouple or pressure transmitter )
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rcsp2689
Inprocess loop measuring Ends can be calibrated . ie., Sensors.. Where else Actuators are Final contol element / Output devices.
Is This Answer Correct ? | 1 Yes | 1 No |
what is a boiler tube leakage detector? ... what is the working principle ?
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
How we connect a instrument with ground, Give brief explanation with help of diagram?
i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
How to calibration of vibration probe
1 Answers Mina Al Ahmadi Refinery,
Why we use 3-15 psi air for control valve input?
how do we commission inergen system?
Specific gravity.
How to Calibrate Level Switch in field
What is feed factor and its Importance in cement industry? How we can solve feed factor?.
why thermocouple called thermocouple?