What is input and output of vaiberation transmitter and what is its unit.
Answers were Sorted based on User's Feedback
your question has different parts. Let I explain you a bit in detail:
1. Input of a vibration transmitter (Proximitor or Oscillator De-modulator) is in shape of frequency which feeds probe or sensor.
2. supply of a Bently Nevada Proximitor is -24 Volts DC. (But now many manufacturers made simple 2 wire vibration transmitters which required +24 Volt DC).
3. Out put of a Proximitor is AC volts and DC volts.
4. AC volts tell us how much is vibration in a shaft/casing, bearing etc where sensor is installed
5. Where as DC voltage indicates how much sensor is away from target. (Target means shaft/bearing etc).
6. These ac volts output of a proximitor is converted at an indicator/equipment to micron Peak to peak or mil Peak to Peak which is units of vibration.(Remember, velocimeter and accelerometer has different units even those also used for vibration sensors)
7. Suppose you have a proximitor with a scale factor
8 volt/mm.
8. Your proximitor output ac voltage is 0.232.
9. Multiply this 0.232 by 353.6, you will get direct microns P-P.
10. Look, 0.232 x 353.6 = 82 microns p-p.
(This all method of proximitor/sensor is called non contact system)
aftabmazari@yahoo.com
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
input for vibration prob is -24v but 24v also possible but they use -24v because its NPN transistor as per bently nevada. then out put is -10v or based on settings.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ujjwal debnath
Output of vibration transmitter is current in mA range & it's
units are mil, micron.
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / iqbal4u87@yahoo.com
vibration transmitter output gap voltage input mils,macrow
Is This Answer Correct ? | 1 Yes | 8 No |
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
What is standard of DCS panel design?and what is step of DCS panel design?wiring and type of connector(screw or DB connector)
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
why we use negative 24vdc to a proximeter
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
how can use ram
WHAT IS THE MASS FLOW FLOW METER
what is the standard controll pressure
What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?
0 Answers Process Control Technologies,
How to calibrate capillary type level transmitter
what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?
What are the characteristics of Control Valve