hi this is noor in my work spot, i arranged THERMOCOUPLE in
the place of RTD. (in FEED WATER tank). can i use T/C or not?
Answers were Sorted based on User's Feedback
Answer / pawan kumar
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range. so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
Is This Answer Correct ? | 27 Yes | 0 No |
Answer / manash ranjan jena
You can use a Thermocouple in place of RTD but you need to
change your control loop instruments accordingly. As T/C
output will be mV where as RTD output is always change in
resistance. Please check the input of your measureing
instrument, if that is a universal input circuit then you
can use a T/C inplace of RTD.
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / manash ranjan jena
For feed water service the process temp. is always below
300 Deg. C. So you can very much use a RTD. And in lower
range RTD is a better solution than T/C. As it has a linear
curve and no compensation required. And even the accuracy
of RTD is better than T/C. However you can very much use a
T/C if the control network allows.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nn
yes, if thermocouple selection is suitable for the
operating temperature. Also you have to check if your
controller supports T/C signal or you have to had seperate
signal converter for that.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / manraj
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range (and also check type of i/p of
ur measuring instrument.) so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mjv
I M AGREE WITH ALL ABOVE ANS..BUT THE MAIN THING IS COST!!
RTD IS COSTLIER THAN T/C..
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / manish tyagi
No T/C are not suitable replaced for RTD because feed water
tank temperature below 120 Deg C (max.).T/C are right used
above 300 Deg C
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / praveen kumar
Yes u can use TC in the place of RTD, but check the
tempeatures range, again there a lot of things to see
whether Thermowell, suits the element or not.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vishok
No. Because in RTD Resistance increases proportional to
temperature. But in thermocouple the output is voltage in
millivolts. So to process such signal you need pre
amplifier, and for RTD U need a bridge circuit.
Is This Answer Correct ? | 4 Yes | 11 No |
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
Name and describe at least 4 status indicators, typically found on a PLC
what happens if we are having very very high cavity and flashing in a control valve..??? is it stops working...immediately... or eroded...slowly
1. What is the main differences between GE Mark IV and Mark V Turbine Control System? 2. what is the main differences between GE Mark V and Mark VI?
If fire would be inside the plant which fire detector is to detected the fire.
I have seen the Temperature element (T/C & RTD) installed in process line on 45 degree position, Why? What it mean? How many types of tapping position for temperature elements?
CAN WE CALIBRATE LEVEL TRANSMITTER USING HART COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER SHELL?
How to calibration coriolis flow meter?
while am calibrating Drager polytron 2IR flame gas detector occured non zero status.how can i get zero status?
When cryogenic control valve will be applied?