hi this is noor in my work spot, i arranged THERMOCOUPLE in
the place of RTD. (in FEED WATER tank). can i use T/C or not?
Answers were Sorted based on User's Feedback
Answer / pawan kumar
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range. so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
| Is This Answer Correct ? | 27 Yes | 0 No |
Answer / manash ranjan jena
You can use a Thermocouple in place of RTD but you need to
change your control loop instruments accordingly. As T/C
output will be mV where as RTD output is always change in
resistance. Please check the input of your measureing
instrument, if that is a universal input circuit then you
can use a T/C inplace of RTD.
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / manash ranjan jena
For feed water service the process temp. is always below
300 Deg. C. So you can very much use a RTD. And in lower
range RTD is a better solution than T/C. As it has a linear
curve and no compensation required. And even the accuracy
of RTD is better than T/C. However you can very much use a
T/C if the control network allows.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nn
yes, if thermocouple selection is suitable for the
operating temperature. Also you have to check if your
controller supports T/C signal or you have to had seperate
signal converter for that.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / manraj
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range (and also check type of i/p of
ur measuring instrument.) so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mjv
I M AGREE WITH ALL ABOVE ANS..BUT THE MAIN THING IS COST!!
RTD IS COSTLIER THAN T/C..
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / manish tyagi
No T/C are not suitable replaced for RTD because feed water
tank temperature below 120 Deg C (max.).T/C are right used
above 300 Deg C
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / praveen kumar
Yes u can use TC in the place of RTD, but check the
tempeatures range, again there a lot of things to see
whether Thermowell, suits the element or not.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vishok
No. Because in RTD Resistance increases proportional to
temperature. But in thermocouple the output is voltage in
millivolts. So to process such signal you need pre
amplifier, and for RTD U need a bridge circuit.
| Is This Answer Correct ? | 4 Yes | 11 No |
WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
how to calculate flow by dp transmitter?
what is basic working principle of Governer in power plant?
What are the key features of a Distributed Control System? describing the various layers (sensor through to business system interfaces) as well as the hardware, software and security aspects of the DCS.
Explain the functions of the CPU of a PLC.
what is difference between OP AMP and differential amplifier?
How will you select suitable Instrument for Process line/Tank/Vessel?
what should be the attitude while answering an interviewer?
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?
In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?
1 Answers Process Control Technologies,
please help me to get the below mentioned quires,which i have to submit for my client.[INSPECTION TEST PLAN] 1]I.T.P for Calibration of all instrument. 2]I.T.P for SS tubing. 3]I.T.P for Fire & Gas devices. 4]I.T.P for CCTV & telecommunication. 5] I.T.P for loop checking.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)