hi this is noor in my work spot, i arranged THERMOCOUPLE in
the place of RTD. (in FEED WATER tank). can i use T/C or not?
Answers were Sorted based on User's Feedback
Answer / pawan kumar
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range. so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
| Is This Answer Correct ? | 27 Yes | 0 No |
Answer / manash ranjan jena
You can use a Thermocouple in place of RTD but you need to
change your control loop instruments accordingly. As T/C
output will be mV where as RTD output is always change in
resistance. Please check the input of your measureing
instrument, if that is a universal input circuit then you
can use a T/C inplace of RTD.
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / manash ranjan jena
For feed water service the process temp. is always below
300 Deg. C. So you can very much use a RTD. And in lower
range RTD is a better solution than T/C. As it has a linear
curve and no compensation required. And even the accuracy
of RTD is better than T/C. However you can very much use a
T/C if the control network allows.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nn
yes, if thermocouple selection is suitable for the
operating temperature. Also you have to check if your
controller supports T/C signal or you have to had seperate
signal converter for that.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / manraj
first of u have to confirm the temperature range in which
you are going to use the thermocouple in place of RTD
becouse the RTD response is better in low range and
thermocouple in high range (and also check type of i/p of
ur measuring instrument.) so if it is a high range then
deffinatly u can go for thermocouple. and u are going for
thermocouple then u have change loop configuration too as
o/p of thermocouple in mV.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mjv
I M AGREE WITH ALL ABOVE ANS..BUT THE MAIN THING IS COST!!
RTD IS COSTLIER THAN T/C..
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / manish tyagi
No T/C are not suitable replaced for RTD because feed water
tank temperature below 120 Deg C (max.).T/C are right used
above 300 Deg C
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / praveen kumar
Yes u can use TC in the place of RTD, but check the
tempeatures range, again there a lot of things to see
whether Thermowell, suits the element or not.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vishok
No. Because in RTD Resistance increases proportional to
temperature. But in thermocouple the output is voltage in
millivolts. So to process such signal you need pre
amplifier, and for RTD U need a bridge circuit.
| Is This Answer Correct ? | 4 Yes | 11 No |
What is the differace between Volumatric flow meter and Mass flow meter.
how to convert transmitter milliamps output to like temp,pressure etc.....
what is the name of thermocople element cable from field to pannel end?
Why all the drains(Gland sealing,ESV,Casing inlet etc) are directly connected to the flash tank instead of hotwell of the condensor in the power plant? My Email Id:naba02222@gmail.com
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
can i use 1 sq mm insted of 1.5 sqmm cable cable length 600 mts under ground laying Cable carrying 24 vdc 4-20ma current
How can I make calculation for Install level transmitter (DP) for open tank and cloes tank?
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
how we can check level probe and controller
What is the relation between electronics & instrumentation
WHAT IS THE VALUE OF MICRON
Consider a control valve action,the inlet air pressure is only 6 ksc but physically how it can be operate against 100 ksc line fluid pressure?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)