why power factor is important?
Answers were Sorted based on User's Feedback
Answer / benu
kva=kw/pf,with low pf,kva will be high,insulation cost in generator and transformer+cu loss in transmission line will rise and efficiency will come down
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / koti
above answer is partially correct i.e, at low pf the kw output is low and is due to inductance and capacitance elements of ckt but not harmonics
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / ghulammohyhuddin
power factor control mager demand form electrical city
because actual lode between appearance lode is power factor
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / purushottam kumar
for constant power and terminal voltage ,if power factor is low current drawn is more ,so more lose ocour ,regulation is poor, conductor size increased than with high power factor
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sudhakar g
Power factor is imp bcoz....ex: If we have an panel that
will give the o/p of 300KW but if we dont maintain the
powerfactor by using APFCR it will give the o/p of 240KW
only....by maintain the powerfactor by using the APFCR we
can get (0.98%)....power factor means something lagging and
leading in power due to harmonics...
Is This Answer Correct ? | 6 Yes | 8 No |
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
what the effect will occur if we increase the airgap in induction motor
what is harmonics?explain in simple words?what is its impact on circuit?
I FINISHED MY B.TECH IN EEE . I AM IN NEED OF A GOOD TRAINING INSTITUTE TO DO COURSES .. CAN ANYONE SUGGEST GOOD CENTRES IN TAMILNADU ,BANGALORE ,OTHER AREAS???????
what is HVDC, what are advantages over conventional system?
what is the difference between circular wdg & ractangular wdg?
can i use 10 mfd + 6 mfd instead of 15 mfd capacitor in single phase motor as running capacitor
What is Fan Coil Unit . How can we calculate CFM .
Load transfer in 11kv double busbar switchgear - operation.
What is Phasing out test?
How to calculate u.p.s load parsentage plz give me formula
What is the distance between body earthing and neutral earthing.?