could i arrange a faulty and healthey battery bank togather
in parallel , if your ans is not then why?
Answers were Sorted based on User's Feedback
Answer / avd
Don't do it. A bad apple can spoil good apples too if kept
together. If you connect good and bad battery bank in
parallel, good battery bank will continuously dicharge in
bad battery bank. Hence there will always be circulating
current between two battery banks. This will make your good
batteries bad very soon.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aree dewan
yes but with this connection the voltage will be constant
bur current will increase.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ankush miglani 09718151073
M NOT SURE BT STILL GIVING MY OPINION.
I SAY YES COZ IF THE TWO BANKS ARE CONNECTED PARALALY THE
OUTPUT WILL BECOME SOMTHING CONSTANT THAN THE O/P OF ONLY
FAULTY BANK. AS THE QUANTITY INCREASED THE RATIO DECREASES.
Is This Answer Correct ? | 0 Yes | 3 No |
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
why ups in kva ratings?
We know flow of electron is current . But why electron flow from negative to positive and current from positive to negative?
What is the diffrence between ofline ups and online ups?
how we can calculate the efficiency of a diesel generator ?
I want to make street light with solar system ... What may I do for procedure and how much of estimation for each material ... If any one knows guide me and inform this id : aravindd7@gmail.com
why the vector group of excitation transformer is YD5(150 deg)how is this factor decided.
What is the function of RCBO? What are the different sensitivity ratings & each application?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
by what factor the starting current is used when comparing star and delta connection for motor starting?
how does this job compare with others you have aplied for?
ro plant grundfos bm30type pump.we start the pump using siemens 3rw 4423-1bc44, 30kw soft starter. bur its failier frequently. so we planed to change the dol starter. sp please tell me any budy its possible or not翿შ†