What happen when the AVR of the generator fails? Will it cause
power instability and total failure of the alternator?
Answers were Sorted based on User's Feedback
Answer / sundar m
AVR is the Automatic Voltage Regulator which is used to keep
the alternator terminal voltage to be constant whenever
voltage drop occurs....by varying the excitation and the
power supplied to the alternator with turbine...If AVR fails
then the voltage level of the alternator fails to be
constant.so the machine will comes out of synchronism.....
Some protection systems are there...to trip the machine when
the AVR fails so dont think like intelligents....
| Is This Answer Correct ? | 34 Yes | 2 No |
Answer / jagan
When AVR fails a protection called Field Failure protection will come into picture and trip the generator.
When AVR trips the machine draws reactive power from grid n continue to run as Induction Generator but above synchronous speed which might damage the turbine.
It has 2 time delays
If Failure of field is associated with under voltage which might happen due to severe fault near the generator and AVR might trip not able to maintain the voltage, the generator is tripped instantaneously.
If the AVR fails and there is no U/V, a delay of 1-2 sec is incorporated hoping the AVR might restore.
PROTECTION ENGINEER 11 YEARS EXP
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rakesh.a.d
When AVR fails,the excitation to the generator fails and the alternator acts as an induction generator taking reactive power from the grid
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheikh
AVR is Automatic voltage regulator. AVR is a vital part of Alternator if Avr has become failed than alternator should gone at shutdown on undervoltage or No volltage safety. its make clear that whenever your enginator reduce the Rpm by any other fault than alternator also going on undervoltage safety that time AVR cannot balanced the determined voltage or Set point voltage.
| Is This Answer Correct ? | 5 Yes | 4 No |
Generally if there is failure of AVR , excitation will switch over manual mode .
| Is This Answer Correct ? | 1 Yes | 0 No |
Further ,the ' loss of excitation relay ' should act to trip . If it does not and the prime mover is still working , then the gen will run as induction generator . It may disturb stability as the pf is very low .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaizad
Generally big power plants have a feature by which the manual rehostate follow AVE. So when Ave trips there is no sudden variations in power and by manual actions can be taken to avoid generator transformer overfluxing by keeping V/for ratio constant
| Is This Answer Correct ? | 0 Yes | 3 No |
Where is the pressure reduce valve in the power plant
a gas turbine have how many thermocouples?
what is the perfect location for furnace draft transmitter in AFBC boiler?
Power plants are called CPP,IPP,LLP What is the meaning of it? And tell me some other type of powerplant names.
why seal air fan is used and where it is used and where is suction taken from
why do you consider yourself a suitable candidate for this position
0 Answers Amazon, Eskom, Nabard,
1 TPH how many Megawatt ?
What is the over speed in turbine? What is critical speed?
What is definition of hydrogen cell?and were are you use?
What are the effects of corona in switch yard.
In a thermal power plant ID Fans running with full load but boiler load is only 80 % give reason ?
9 Answers Essar, Prumatech, Tata Power,
why drum level is increased when one of the running coal elevations are suddenly tripped?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)