I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
Is This Answer Correct ? | 1 Yes | 0 No |
minimum ohm for lighting minimum ohm for Earthing
IS THERE ANY ELECTRONIC CIRCUIT TO REDUCE THE NEUTRAL TO EARTH VOLTAGE BELOW 3V ?
what is diversity factor ? plzzzzzz describe me
how the alternator transfere mechanical energy to electrical one ??
1.wat is the negative slip region in the motor?
How can I known multiplying factor .without multiplying table
What is the formuala to calculate the rating of motor protection circuit breaker
what is resver in electrical enginnering with answer
what i the full form of ABS 111 in transformer.
what are the different methods for the starting of a synchronous motor.
What is the function of turbo charger in generators
Explain the experiment on ward leonard method of speed control of a dc shunt motor.