I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
| Is This Answer Correct ? | 1 Yes | 0 No |
why we are called the 4-20ma transducer,not 0-20 ma transducer??
List the advantages of star-delta starter with induction motor?
For maintenance Department What type documention requir for ISo & TS audit
1 Answers Megatron Solutions, Sams,
Who are the manufactures those manufacturing 3Cx2.5sqmm FRLS cables. I heard about FRLS technology adopted only in wires useful for wirings
what is the difference between ups & inverter
4 Answers Cushman Wakefield, Dana Group,
Welding machine
How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?
what is GRR(Grid Rotot resistance)?Why it is used beside of LRS?
9 Answers ACC, L&T, Sri Biotech,
Transformer's core is made up of which material and why so?
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
Testing procedure of DG alternator stability test
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)