Answer / huzy
This relay continuously supervise the healthiness of tripping circuit.It gives an alarm for Open / short tripping coil or tripping supply failure.
| Is This Answer Correct ? | 44 Yes | 4 No |
Answer / raghavendran.r
I would like to add more on the previous answer.As stated
earlier trip circuit supervision relay will monitor the
proper functioning of trip circuits based on the feedback
signal obatained from the tripped circuit.if the circuit
has not tripped even after getting trip command,then as a
preventve measure sometimes LBB ie local breaker back up
will act upon to prevent any further damage to the system
due to any fault.
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / hanuman
trip circuit supervision relay is the relay which
supervises the trip circuit of the circuit breaker. It even
tests wheather dc supply to trip circuit is under proper
condition or not. some times trip circuit gives signal to
circuit breaker, but circuit breaker doesn't break the
circuit, then supervision relay makes circuit to break by
LBB.
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / k.prakashchandra
This relay is used to supervise the tripping circuit and to
provide alarm ,independent of breaker status, for 1)loss of
dc supply2)faults in trip coil or cables 3)faults on the
breaker aux contacts 4)faults in the relay itself
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / balaji
This Relay will monitor over All the tripping circuit's healthy condition and will provide alarm in tripping circuit unhealthy also Can be utilize multi level.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nitin bhati
as its name indicate ...it works like a supervisor used to control the complete tripping circuit if there is a fault in controlling supply (dc) it sense it and gives a command to breaker.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is reactive power (MVAR) and how it is control? how it is generate in powerplant?
what is the reason for balance of voltage in magnetic balance test?
What is the difference between CT for protection and Ct for metering?
What is rated value? is it phase values or line values?
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.
there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
5 Answers Construction, wbsedcl,
how much current and power in watts can be carry by 2.5^2mm cu wire and 4 core 10^2mm Al cable?
what is LOS(line of sight)?
XYZ
how can calculated the rating of the 11 KV transformer?
if one potential missing in energy meter , how much % slow the energy meter?
What is pole of the system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)