what is mean by live zero and dead zero
Answers were Sorted based on User's Feedback
Answer / bunny
Suppose the range of process variable is
(0-150)PSI.So when the input is zero,the value in
instrument,say a transmiter connected to measure the
pressure,will shows 4mA.This is live zero.i.e,even if the
input is zero,output has some value.
Lets assume the instrument is faulty or the
power supply to the instrument is cuts off.Then it will
show zero reading.This is called dead zero.i.e,when the
instrument is faulty,it will shows the real zero value.
Is This Answer Correct ? | 37 Yes | 3 No |
Answer / devendra_kushwaha27
Live Zero means 4MA
Dead Zero means below 4 MA
Is This Answer Correct ? | 26 Yes | 12 No |
Answer / inzamam
When the working instrument shows zero as its output ....it is called as live zero........
When the instrument fails , thereby showing zero as their output , it is called as dead zero .
Is This Answer Correct ? | 1 Yes | 2 No |
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
how many types of preheaters are in cement industry & what r they can any body explain?
What are the problems faced while testing HART instruments?
how to calibrate level transmitter
What is sensitivity in vibration probes..?
please help me to get the below mentioned quires,which i have to submit for my client.[INSPECTION TEST PLAN] 1]I.T.P for Calibration of all instrument. 2]I.T.P for SS tubing. 3]I.T.P for Fire & Gas devices. 4]I.T.P for CCTV & telecommunication. 5] I.T.P for loop checking.
tell about various protocols used in different plcs
What should be the ideal tapping location for pressure differential transmitter for liquid service. If the tapping taken from the top of the pipe then PDIT will work properly or not. If PDIT do not work properly then what minimum corrective action should be taken in order to solve wrong tapping locations.
hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank). can i use T/C or not?
What is i/e or o/p transmitter(ma/v)?
How to connect PLC to DCS ?
I need circuit for RTD senser?