How we will check whether the proximity, which we have is
either NPN or PNP, if no data sheet or manual or any
details is available to us ???
Often identification data is printed on proximity (or prox) sensor's label but it is not uncommon for the label to damaged, missing or unreadable.
Many prox sensors are DC powered, 3 wire devices that conform to a standard wiring color code:
brown is (+) supply voltage, typically 24Vdc
blue is (-) supply voltage common or return
black is the sensor's switched output
To test a 3 wire sensor to determine whether it is a PNP or NPN type you need a DC power supply and a DC voltmeter.
Set the meter to DC voltage to a range greater than the supply voltage (typically 24Vdc), like 50/100/200/600V
The black meter probe should be in the 'common' meter socket
The red meter probe should be in the DC 'volts' socket
Connect the sensor's brown wire to the power supply (+)
Connect the sensor's blue wire to the power supply (-).
Turn the power supply on.
Ensure that the prox sensor is not triggered by presence to an object.
Connect the black meter probe to the blue sensor wire.
Connect the red meter probe to the black switched signal output sensor wire.
If the meter is connected to a PNP device, the meter will read 0V.
If the meter is connected to an NPN device, the meter will read 24Vdc.
Force the sensor to change state/output by detecting an object.
- If it is an inductive proximity switch, place a piece of metal in front of the sensor.
- If it is a photoelectric sensor, block the photoelectric beam.
- For an ultrasonic sensor or a capacitive sensor, you can just use your hand to make the sensor output. Some prox sensors use an LED that lights up when the sensor detects an object.
With an object present, a PNP device's output will change and the voltmeter readout will read 10V to 30V. This is also known as a "sourcing" device.
With an object present, an NPN device's output will change and the voltmeter readout will be 0V. This is also known as "sinking."
Another test to check for PNP:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.
When sensing no object, the signal output will be 10V to 30V.
When sensing an object, the signal output will be 0V.
Another test to check for NPN:
Connect the power supply (+) to brown, (-) to blue.
Connect the red meter probe to the brown (+) sensor wire.
Connect the black meter probe to the sensor's black signal output wire.
When sensing no object, the signal output will be 0V.
When sensing an object, the signal output will be 10V to 30V.
Is This Answer Correct ? | 3 Yes | 0 No |
if RTD damage in plant, how we know?
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
What is the difference between PLC-HMI and DCS as each function of DCS based system is possible in PLC ?
If The RTD(PT100) Show .776 Kohm Resistance the Temperature of process fluid how much?
Why ues 250 ohms Resistor during hart type instruments calibration with hart protocol in details ?
I want to measure and control level in tank of size 10*5 filled with gasoline, so plz give me the solution with clear details. how to select transmitter and sensors.
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
what is differences between singal acting and double action valve
1 Answers Carlo Gavazzi, Welspun,
what is meant by calibration
List three types Level Gauges with their working principles
describe yourself?
What pressure results for a flow transmitter of range 0- 180t/h in the dcs and 0-301mbar in the field using square root extraction. Kindly also suggest formulae for the percentages 0,25,50,75,100?