how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?
Answers were Sorted based on User's Feedback
Answer / komal
1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ashwin jain
if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / haridass
1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.
2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mr.georgemathews
It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.
The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.
This whole process will hardly take 5 min.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between ROM & RAM .
what is diff between sensors and transducers.explain with ex?
Why do we go for 4-20mA? why not other standara?
what is the calibration procedure for magnetic flow meter @ onsite
Can we use twisted pair cable instead of ethernet for communication?
what is isloted barrier how it works and what are the main purpose.how it make safe area.
could someone explain for me what is 32-bit Floating Point ? Thanks
What are different types of valves?
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
Difference between dcs and plc including date processing and architecture.
what is the differnce between PLC & DCS
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?