how to rectify the problem ,if we erected the DPT instrument
wrongly of hp on lp side and lp on hp side?
Answers were Sorted based on User's Feedback
Answer / komal
1)Remove and re install correctly
2)Change calibration range if presently set as 0 to 1000
mmH2O to 1000 to 0 mmH20 and make required changes in
control system to see it correct.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / ashwin jain
if hp is on lp side & lp is on hp side then dpt show negative reading...
to rectify just remove & reinstall the DPT.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / haridass
1. The easy physical way, turn the dp cell 180 degrees and
connect the fittings and tubings.
2. Check the LRL/URL using HART comm, if the range of the
transmitter is capable mean change the LRV/URV.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mr.georgemathews
It is a common mistake to connect the lp side to the hp side
of the DPT and the Hp side to the Lp side of the DPT. SO we
need not to worry.
The solution is to remove the impulse connection from the
DPT , make a 180 degree turn of the diafram, which is the
connection mode of the DPT. If u see it you can see there
are holes on the opposite side also (H & L). which is just
the opposite to front side(L & H). SO no u can connect the
impulse line out here. And also we better recalibrate the
DPT Using HART Communicator.
This whole process will hardly take 5 min.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
no problem when DPT transmitter wrong leg hp and lp mount the transmitter will show the negative indication
so you not remove the transmitter but only re-range the transmitter value with hart communicator on lp side put negative and hp side positive range
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?
whats the diff b/w zero pressure and obsolute pressure
radial & axial vibration sensor output voltage is ac or dc volt?
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
Difference between dcs and plc including date processing and architecture.
What is first echo & echo window in radar type level transmitter?
list of flame proof certification ?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
please someone tell me what is function of vibration sencer and how many types and how to control viberation.please. my id is jimmykhan077@gmail.com
difference between null and deflecting instrument.
Shall we get the reading on level transmitter only by termination,without commissioning?
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)