If a differential pressure transmitter is calibrated for
0~2500 mmH2o and transmits a 4~20mA dc signal. The
transmitter is placed across an orifice plate which is sized
to create 2500 mmH2o differential at 5000m3/Hr
a) what is the flow rate when the transmitter signal is
13.0mA DC?
b) what is the signal output of the transmitter when flow
rate is 2500 m3/Hr ?
Answers were Sorted based on User's Feedback
Answer / nani babu
a) flow rate for 13mA is 2812.5 m3/hr
b) 12 mA to 2500 m3/hr
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / nabil amrani
a) Y=(20-4)/(5000-0)*x + b=16/5000*x + 4
when y = 13 mA x = (13-4)* 5000/12 = 2812.5 m3/Hr
b) Y=16/5000 * x + 4
when x= 2500 y= 16/5000 * 2500 +4 = 12 mA
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / raju
ans a)=√(13-4/16)×5000=3750 m3/hr
b)=(2500/5000)×(2500/5000)×16+4= 8 mA
| Is This Answer Correct ? | 13 Yes | 13 No |
a flow transmitter [range-0-400mbar] connected in process line. please explain me how to calibrate the flow transmitter , & how to do static error
what is plc?
27 Answers HPCL, KRL, Noor Company, Petrochemicals, SS Automation,
what is the difference between attemperator and desuperheater ?
what is different between modbus and serial link? please could anybody give right answer.
What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?
What is possitive and negative feedback?
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
what is mean by live zero and dead zero
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
What is the difference between ff transmitter and non ff transmitter
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)