what are the difference between conventional and smart transmitter.
Answer / carl_ellis
Smart vs Conventional transmitters
Conventional
A conventional 4-20ma transmitter regulates the loop
current and provides only a process variable signal.
The zero and span adjustments are analog adjustments. n
the case of fixed range transmitters the zero and span
adjustments are limited to about plus/minus 2-3% of the
fixed zero or span values. Some conventional transmitters
have an adjustable turndown range, but calibrating a
turndown range requires a simulated process variable (an
applied calibration pressure or a simulated temperature
(RTD or thermocouple) electrical signal). Turndown is
generally limited to about 5:1 or 6:1.
Smart
A smart transmitter provides a process signal but can also
send/receive information about the instrument itself, e.g.
zero and span info, tag (instrument loop identification),
diagnostics, or even multiple process variables using a
digital protocol.
Configuration changes are done either with a keypad and
display or through a protocol like HART, which is
superimposed on the 4-20mA signal, so no additional wiring
is needed for smart communication. HART communication is
accomplished with a handheld communicator or a modem and
software.
Turndown rangeability can be as high as 100:1 (with reduced
accuracy at the low end); 15:1 or 20:1 with stated accuracy
and can be accomplished without applying an external
calibration signal, reference or supply.
Smart transmitters can communicate via a Fieldbus,
Foundation Fieldbus or Profibus.
Carl Ellis
Measure First
| Is This Answer Correct ? | 20 Yes | 4 No |
HOW TO CALIBRATE A DRUM LEVEL TRANSMITTER
what is the current pay package for an instrumentation engineer having 2 years of experience in cryogenic technology???????
what is pt100 RTD, and does 100 stands for
what is dry leg and what is wet leg?
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
how to calibrate transmitter
How we select the range of level transmitter in closed vessel ?
Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =
few questions on RS 232,1 question on relationship of impedance and turns ratio, many questions on flowmeters
could someone explain for me what is 32-bit Floating Point ? Thanks
If the on Of the DO module is off in the System cabinet, then what is the Procedure to check weather the Module is working or not.
What are the processes Variables?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)