Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

Answers were Sorted based on User's Feedback



WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / welcome4ujd

you can use fluke milliampre simulator tocalibrate a
controlvalve through i/p converter, ot by using a druck
pressure calibrator directly to the controlvalve positioner.

Is This Answer Correct ?    30 Yes 1 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / upendrae

we can use the 4-20ma source for calibration of the electro
pneumatic valves.

Is This Answer Correct ?    13 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / tarun

CONTROL VALVE HAVE MOSTLY 3 PART BODY,BONNET AND
ACTUTOR,CONTROL VALVE REQUIRED AIR SUPPLY 20 PSI OR 140KPA
AND SIGNAL 4TO20MA AND TOOLS AND STANDURD P.G OR DRUCK. SO
FINNALY WE USE ENOMET SOURSE, DRUCK, OR REGULATOR AND AIR
SUPPLY REQUIRED

Is This Answer Correct ?    9 Yes 2 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / murugesan

First ensure both I/P and positioner air supply are as
it should be before starting up control valve
calibration/stroke checking activity. Then take any of loop
or multifunction calibrator based on the instrument
availability in your plant for Ex 707Ex, UPS-III-IS, UPS-
II, UPS-IS, DPI610 IS (connect series with 24 VDC supply),
UNOMAT and 725Ex

And select “mA source with 24V DC” option and connect 4-
20mA source to I/P converter and simulate appropriate mA to
check the stroke. Normally control valve stoke checking is
called as control valve calibration.

Is This Answer Correct ?    2 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / rushikesh s gaddpawar

CONTROL VALVE CALIBRATATION MANLY USE MA POWER SUPPLY
SOURSE TO CALIBRATE CONTROL VALVE

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / balu

WE CAN CALIBRATE IT THROUGH A MILLI AMPS FEEDER IN PRESENT
DAYS

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / ali faozy

if the control valve has i/p &postioner we need [ 4 to 20 ]
milliamper dc source , 140 kpa air supply for i/p and 700
kpa for positioner [depending on positioner supply
recommendation]
we need also to calibrate the strock indicator for fully
open and fully close positions
if the control valve has no i/p & positioner then we need
air signal source of [20 to 100]kpa depens on control valve
design
and 700 kpa air supply for valve supply

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / shabbir ahmad mughal

we use loop calibrater and miliampere source for
(pst)partial strok testing or calibration of control valve

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Can I calibrate the Electromagnetic Flow Meter on line and How.

0 Answers   SEWA,


what is reset windup in integral control?

6 Answers   Honeywell,


How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?

2 Answers   QAFCO,


why the steam drum and deaerator level transmitter range is in negative MMWC to zero

3 Answers   Emerson, Jindal, JKPM,


how in the 2 - wire transmitter, 24v supply and the 4ma signal gets in the same path?

1 Answers   Yokogawa,


Can any body tell me about SAP MAINTINANCE MODULE. WHAT IS its function and application. And study material Source about it. I shall be very thankful.

0 Answers  


Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?

0 Answers   AquaTech,


Please can anybody help for control valve sizing step by step procedure?

0 Answers  


what is intools software

2 Answers  


what are the basic instructions used in simatic s7-300 plc?

5 Answers   Dr Reddys, HZL, Siemens,


In bently nevada vibration monitoring system,what is the reason to maintain the Resistance of the probe + extension cable equal to 95 ohm? If possible explain the basic principle of measurement with detail electronic circuits.

0 Answers   Essar,


how u calculate ai/di/ao/do capacity in ur dcs?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)