WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
Answers were Sorted based on User's Feedback
Answer / welcome4ujd
you can use fluke milliampre simulator tocalibrate a
controlvalve through i/p converter, ot by using a druck
pressure calibrator directly to the controlvalve positioner.
| Is This Answer Correct ? | 30 Yes | 1 No |
Answer / upendrae
we can use the 4-20ma source for calibration of the electro
pneumatic valves.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / tarun
CONTROL VALVE HAVE MOSTLY 3 PART BODY,BONNET AND
ACTUTOR,CONTROL VALVE REQUIRED AIR SUPPLY 20 PSI OR 140KPA
AND SIGNAL 4TO20MA AND TOOLS AND STANDURD P.G OR DRUCK. SO
FINNALY WE USE ENOMET SOURSE, DRUCK, OR REGULATOR AND AIR
SUPPLY REQUIRED
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / murugesan
First ensure both I/P and positioner air supply are as
it should be before starting up control valve
calibration/stroke checking activity. Then take any of loop
or multifunction calibrator based on the instrument
availability in your plant for Ex 707Ex, UPS-III-IS, UPS-
II, UPS-IS, DPI610 IS (connect series with 24 VDC supply),
UNOMAT and 725Ex
And select “mA source with 24V DC” option and connect 4-
20mA source to I/P converter and simulate appropriate mA to
check the stroke. Normally control valve stoke checking is
called as control valve calibration.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rushikesh s gaddpawar
CONTROL VALVE CALIBRATATION MANLY USE MA POWER SUPPLY
SOURSE TO CALIBRATE CONTROL VALVE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
WE CAN CALIBRATE IT THROUGH A MILLI AMPS FEEDER IN PRESENT
DAYS
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ali faozy
if the control valve has i/p &postioner we need [ 4 to 20 ]
milliamper dc source , 140 kpa air supply for i/p and 700
kpa for positioner [depending on positioner supply
recommendation]
we need also to calibrate the strock indicator for fully
open and fully close positions
if the control valve has no i/p & positioner then we need
air signal source of [20 to 100]kpa depens on control valve
design
and 700 kpa air supply for valve supply
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shabbir ahmad mughal
we use loop calibrater and miliampere source for
(pst)partial strok testing or calibration of control valve
| Is This Answer Correct ? | 0 Yes | 0 No |
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
In the field and in the control room different power supplies if used How to handle the ground
What is the procedure of calibration of Load cell?
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
how to make temperature closed loop
Relation in MMWC to Flow rate
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
what is the working principle of dis-placer type level transmitter
give me the formula for analog to digital converter and also d to a converter
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
What is loop checking ?
10 Answers Kharafi National, Petrofac, Samsung,
how to check thermocouple ,its working or not?
14 Answers Coca Cola, Ford, Honeywell,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)