WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
Answers were Sorted based on User's Feedback
Answer / welcome4ujd
you can use fluke milliampre simulator tocalibrate a
controlvalve through i/p converter, ot by using a druck
pressure calibrator directly to the controlvalve positioner.
| Is This Answer Correct ? | 30 Yes | 1 No |
Answer / upendrae
we can use the 4-20ma source for calibration of the electro
pneumatic valves.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / tarun
CONTROL VALVE HAVE MOSTLY 3 PART BODY,BONNET AND
ACTUTOR,CONTROL VALVE REQUIRED AIR SUPPLY 20 PSI OR 140KPA
AND SIGNAL 4TO20MA AND TOOLS AND STANDURD P.G OR DRUCK. SO
FINNALY WE USE ENOMET SOURSE, DRUCK, OR REGULATOR AND AIR
SUPPLY REQUIRED
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / murugesan
First ensure both I/P and positioner air supply are as
it should be before starting up control valve
calibration/stroke checking activity. Then take any of loop
or multifunction calibrator based on the instrument
availability in your plant for Ex 707Ex, UPS-III-IS, UPS-
II, UPS-IS, DPI610 IS (connect series with 24 VDC supply),
UNOMAT and 725Ex
And select “mA source with 24V DC” option and connect 4-
20mA source to I/P converter and simulate appropriate mA to
check the stroke. Normally control valve stoke checking is
called as control valve calibration.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rushikesh s gaddpawar
CONTROL VALVE CALIBRATATION MANLY USE MA POWER SUPPLY
SOURSE TO CALIBRATE CONTROL VALVE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
WE CAN CALIBRATE IT THROUGH A MILLI AMPS FEEDER IN PRESENT
DAYS
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ali faozy
if the control valve has i/p &postioner we need [ 4 to 20 ]
milliamper dc source , 140 kpa air supply for i/p and 700
kpa for positioner [depending on positioner supply
recommendation]
we need also to calibrate the strock indicator for fully
open and fully close positions
if the control valve has no i/p & positioner then we need
air signal source of [20 to 100]kpa depens on control valve
design
and 700 kpa air supply for valve supply
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shabbir ahmad mughal
we use loop calibrater and miliampere source for
(pst)partial strok testing or calibration of control valve
| Is This Answer Correct ? | 0 Yes | 0 No |
without a positionar can a control valve operate? give the difference of operating with positionar and without positionar?
what should he know if he is an assitent engineer instrumentation in cement industries of experience of 10 - 15 year.
What are the types of valves?
what is the main supply source for pressure transmitter?
hi everybody. right now i am working with thermal power plant. our company plant is tripped because of program corrupt. i would like to know is it possible when the plant is running. we are using FREELANCE ABB800F CONTROLLER.
What is CNC
how to calibrate Necleuonic level transmitter.?
what is maxdna ?. explain about the software details.
Can anybody please let me know Orifice plate sizing calculation formula and step by step procedure
why r using 250 resistances
How can SmartPlant Instrumentation users take advantage of these global services?
hello dear i have faced problem in drum level transmitter. the problem is when i engrize the meter meter shows 100% but the actual level 40 or something plz suggest me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)