To test Transformer we give HT side 440V to see wheather
that it is producing 17.6V on LT to verify Voltage ratio is
correct or not but when we give the 440V voltage to LT side
then what will happen to HT voltage ?
Answers were Sorted based on User's Feedback
Answer / manohar mishra
For ratio test, only the change in voltage is to be measureD. If 440 V is fed to LV, HV voltage will go to a HIGH VALUE (11kV) making it difficult to measure. Blowing of fuses do not occur as there is no flow of current.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / nithi
For ratio-test,the second answer may be correct.
But at the same time,if we apply high voltage in LV
side (in ratio-test also)for a longer period (in seconds),
LV winding cannot withstand, result in insulation break-
down,blown-out of fuses.
generally ratio-test is conducted with the
specified (allowable) voltage magnitude.so,practically this
much of voltage is not applied for LV side.I hope,this
answer will be correct.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nithi
Nothing will happen.Simply,fuse will blown-off.
REASON: LV windings normally have low resistance (fatty
winding) compared to HV side.so, at the moment of
application of high voltage the fuse will sacrifice itself
to pretect the transformer LV windings.
Is This Answer Correct ? | 0 Yes | 4 No |
what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.
how does high earth to neutral voltage affect electronic equipment?
which loses are in transformer .explane each loses
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
how to diffrentiate between ac & dc motors from a distance
i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors
What is the significance of vector grouping in Power Transformers??
what are the types of basic earthing?and why we are doing that?
I have calculated load for an office building which is 1200 KW as all the load is single phase therefore its 1200 kw single phase. Now i have to design Transformer and Generator for this load Please kindly give me exact answer that how much capacity of Three Phase Transformer and Three Phase Generator is required for this load.
what is the function of CRGO in a Transformer?
hello, I need to know exactly what happen in the motor while it is connected to the (star/delta) starter, mechanical and electrical. Thaks for answering
1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?