Answer / venkat boyi

The rating of any electrical device is based on losses
developed in the machine.In Transformer the losses depends
up on only Voltage and current but not on PF, hence the
rating of it is in KVA. In motor the output is mechanical
and mechanical load represented by HP in Watts

Is This Answer Correct ?    44 Yes 2 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sudhir singh

the rating of any machine depend the losses.The losses in
transformer which are iron and cupper losses depend upn the
current and voltage and not on their product so its rating
is in kva not in hp.
As motor gives mechanical output which is measured in hp.

Is This Answer Correct ?    16 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sekar

for transformer we can connect any load(R,L).so its power
factor variable . so it is in kva...
since motor is a load .It is designed for particular power
factor.

Is This Answer Correct ?    5 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / h r jadhav

transformer handels electrical energy matching to the
system which containing active and reactive power .which
measured in volt amp capacity.hence rated as mva or kva.how
ever electric motor is meant for converting electrical
energy into mechanical energy that is shaft power . and
shaft power is always rated in horse power .

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / om prakash rai

in transformer only two losses is consider one core loss and
other copper loss and core load is depend on the voltage(v)
and copper load depend on the current(i),so we know the
rating of every system is dependent on his system loss so
transformer rating in KVA .in moter,the output of moter is
mechnical so its rating is always consider in HP.

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / sudhi

The rating of any electrical device is based on losses
developed in the machine.In Transformer the losses depends
up on only Voltage and current but not on PF, hence the
rating of it is in KVA. In motor the output is mechanical
and mechanical load represented by HP in Watts

Is This Answer Correct ?    1 Yes 1 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / chandresh

transformer losses depends on the load does not include power factor, motor include power factor

Is This Answer Correct ?    0 Yes 0 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / david wilson

By convention:
Power supplies are rated for their capacity to output power and are rated in VAs or kVAs.
Loads are rated for their power consumption and are rated in hp (In Europe they would be rated in Watts or KW as metric units).
For the purposes of ratings, transformers are rated based upon their ability to supply power to a load and so are rated in VA.
A 1kVA transformer can drive a motor of up to 1.34 hp (1kW).
Note: It the transformer was rated by the power it consumed (the losses when 1KW is drawn from the output) it would be more difficult to figure out what size of transformer you need to drive your 1.34hp motor.

Is This Answer Correct ?    0 Yes 0 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / yogee.basu

1.Transfomer is a balance load ,( trere is no change in
pf,frequnce, and load)
2.Motor is a un balance load (it is change in pf,frequnce,
and load)

Is This Answer Correct ?    16 Yes 26 No

1. Why transfomer reting in KVA and Motor in HP..

Answer / gunasekaran

for transformer it is electrical load. but motor is
machanical load so it is HP transformer in VA

Is This Answer Correct ?    6 Yes 21 No

Post New Answer

More Electrical Engineering Interview Questions

what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc

2 Answers  


I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.

1 Answers  


How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side

0 Answers  


Hi to u all : Friends: Why when operate on 2 phase welding machine the power metr goes reverse ?? the meter is god on other loads. thanks

2 Answers   Gedco,


what r the sizes of CB's? how to select CB's?

1 Answers  






How to put breaker in service / test position.

1 Answers   KSEB, L&T, Siemens,


what is unit of inductance

12 Answers   Bhel, Bosch, OSML, Vijai Electricals, Voltage,


what is excitation system explain in detail with its working?

1 Answers   Toshiba,


Office , overtime and television how big this stage?

0 Answers   ONGC,


what is the difference b/w KVA and KW? the transformer are mentioned KVA rating and the loads are mentioned KW.why?

2 Answers  


what is the 2MVA distribution transformer efficiency

1 Answers  


WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)